Yes, I guess I will change the Lower Zones 3.3K to the 3.74K and the Upper Zones I will add the 6.98K. Just have to put them in the Control Panel since they are not being used except for Zones 9 and 10.
I checked the other forum that you sent me the link to. Only got one answer, and that was to change resistors on all the Zones even if they are not used.
Hello Again
I understand what you are saying about the resistance tolerance in the zone circuits. I will change out all the 3.3k resistors with a 3.74k for zones 1 -7. I will leave zone 8 a 680 ohm because it is designated as a Fire Zone, in Location 37 Segment 6. If it were not turned on as a...
Thank You for the information. I gave it a try by turning on the double zoning feature. All zones except zone 8 which is a fire alarm have a 3.3k EOL resistor. The zones 9 & 10 have a 6.98k EOL resistor. According to the manual it calls for a 3.74k on the lower zones when doubling. I went to...
I have a NX-8v2 Security System and want to know if I use the double zoning feature will I need to change all the EOL resistors. I wanted to add only two zones so if I turn on zones 9 and 10 only in Location 28 and change those resistors will the other zones be effected if I do not turn them on...