Hi All,
I've got a question regarding the physical size of transformers.
I have a transformer configured as an oscillator that is driving a load that
is mostly capacitive but has some resistance. The max output voltage is 100V
AC, and the max current is 0.7A AC, at 300Hz. So the VA value is 70 VA. The
real power delivered is 25W.
I need this transformer to be as small as possible, so I'm wondering what
the main factor is in determining its physical size. Is it resistive losses
in the windings heating up the transformer which it needs to dissipate to
remain cool enough to run, or is it core size needed to store the energy per
cycle, or core losses heating it up?
I am actually thermally bolting the whole thing to a very large heatsink
which is fan cooled, so this would increase the heat the tranformer could
generate while still maintaining a working temperature. In that case, is it
simply down to the core size needed to store the energy transferred per
cycle which will determine its size?
Thanks!
Mark.
Martin Riddle
markp said:
Hi All,
load that is mostly capacitive but has some resistance. The max output
voltage is 100V AC, and the max current is 0.7A AC, at 300Hz. So the
VA value is 70 VA. The real power delivered is 25W.
what the main factor is in determining its physical size. Is it
resistive losses in the windings heating up the transformer which it
needs to dissipate to remain cool enough to run, or is it core size
needed to store the energy per cycle, or core losses heating it up?
heatsink which is fan cooled, so this would increase the heat the
tranformer could generate while still maintaining a working
temperature. In that case, is it simply down to the core size needed
to store the energy transferred per cycle which will determine its
size?
Thanks!
Mark.
Core size and core losses. Laminate manufactures will specify losses in
Watts per Pound (W/lb)
If you can get away with higher magnetizing current and higher core
losses then the Core area will be less.
But then your winding losses will increase too, if you increase turns to
compensate for less core ;(
Transformer design is part art, and empirical design.
Cheers
Tim Williams
There is value in adding an inductor across the load (or in series, as the
case may be) to cancel out the substantial reactive power. The closer to
1.0 your power factor is, the easier it is to transform.
Tim
Ross Herbert
::> Hi All,
:> I've got a question regarding the physical size of transformers.
:> I have a transformer configured as an oscillator that is driving a
:> load that is mostly capacitive but has some resistance. The max output
:> voltage is 100V AC, and the max current is 0.7A AC, at 300Hz. So the
:> VA value is 70 VA. The real power delivered is 25W.
:> I need this transformer to be as small as possible, so I'm wondering
:> what the main factor is in determining its physical size. Is it
:> resistive losses in the windings heating up the transformer which it
:> needs to dissipate to remain cool enough to run, or is it core size
:> needed to store the energy per cycle, or core losses heating it up?
:> I am actually thermally bolting the whole thing to a very large
:> heatsink which is fan cooled, so this would increase the heat the
:> tranformer could generate while still maintaining a working
:> temperature. In that case, is it simply down to the core size needed
:> to store the energy transferred per cycle which will determine its
:> size?
:> Thanks!
:> Mark.
:Core size and core losses. Laminate manufactures will specify losses in
:Watts per Pound (W/lb)
:If you can get away with higher magnetizing current and higher core
:losses then the Core area will be less.
:But then your winding losses will increase too, if you increase turns to
:compensate for less core ;(
:Transformer design is part art, and empirical design.
:Cheers
My old design engineer (now deceased) was a reasonable hand at what we
technicians called the "black art" of transformer design. He always said it
usually took at least 3 iterations to develop the most ideal solution for any
transformer. Using all the transformer design theory and tools will rarely
produce what you want at the first attempt.
U
Uwe Hercksen
the minimum necesary weight of the core is proportional to the power
transferred and inverse proportional to the frequency. If the windings
with a wire thick enough for low resistive loss does not fit into the
core you will nead the next larger one. If you want the transformer to
be as small as possible, try to make the power as low as possible and
the frequency much higher than 300 Hz. Avoid high voltages requring a
lot of windings and extra isolation.
Bye
U
Uwe Hercksen
markp said:
So if I were to try to estimate the size of a 400Hz toroid (just core size,
ignoring windings for now) for a given VA rating, I could look at a 50Hz
mains version and halve all the dimensions x, y and z to give 1/8 volume?
or simply select a core with 1/8 of the mass. It is not necessary to
halve all dimensions exactly, enough mass of the core is important.
Bye