G'day I have a 9600 series Weiken VFD that we were using in a farm. The VFD incoming was struck with lighting and blow the Full Bridge Rectifier off. I've got it replaced and the drive display and everything was working.
I tried to get the pump to run and it was initially working for maybe 5 minutes before I shut it down.
I then turn it off and try to run the pump again but this time the VFD wont reach 50 Hz (fluctuating around 46-47 Hz) the pump was going crazy with pressure fluctuating between 10-20 kPa (Normally operating at 15 kPa steady @ 50 Hz).
I disconnected the pump and from the VFD display I can see it going up to 50 Hz without the pump connected.
Initially thinking that the pump might be broken I then put the motor on DOL via MCB and the pump runs just fine maintaining 15 kPa.
That leads me to think that the VFD is broken however I've got no idea what else I can check with the VSD does anyone else have similar issue before with any VFD?
I've tried the IGBT testing method but no luck for me. Please help..
I tried to get the pump to run and it was initially working for maybe 5 minutes before I shut it down.
I then turn it off and try to run the pump again but this time the VFD wont reach 50 Hz (fluctuating around 46-47 Hz) the pump was going crazy with pressure fluctuating between 10-20 kPa (Normally operating at 15 kPa steady @ 50 Hz).
I disconnected the pump and from the VFD display I can see it going up to 50 Hz without the pump connected.
Initially thinking that the pump might be broken I then put the motor on DOL via MCB and the pump runs just fine maintaining 15 kPa.
That leads me to think that the VFD is broken however I've got no idea what else I can check with the VSD does anyone else have similar issue before with any VFD?
I've tried the IGBT testing method but no luck for me. Please help..