I was looking at a power supply on a big server box the other day and noted
just how much power it seems to be wasting (presumably as heat as opposed
to some other means like microwave radiation or flashing lights). It had a
listing with two voltage ranges, 100V-127V at 11.6A and 200V-240V at 4.8A.
I've seen several other power supplies, mostly from online tech specs, that
either show some level of increased efficiency at the higher voltage(s), or
at least no difference. Or is this really efficiency? Perhaps could it be
the case that it simply can provide a little more current on the DC side
when operated from the higher voltage? Any possibility that it's really a
frequency issue (e.g. more efficient at 50 Hz for some reason)?
I really think this is increased efficiency at higher voltage due to higher
currents at the lower voltage causing more heating. The few samples I have
seen don't really give me a good sense of how widespread this is, and how
much is lost over all power supplies on average. Anyone else have any real
figures for this?
The National Electrical Code used in the USA has a restriction 210.6(A)(2)
that limits the voltage between conductors to 120V for circuits supplying
cord-and-plug connected loads using 1440V or less, in dwelling units. This
a restriction I would like to see removed, or at least made substantially
lower, so that people in the USA can have circuits to power computers that
can run at a higher voltage for more efficiency, if they choose to do so.
Otherwise people wanting to do this would have to either violate the rule,
or be clever and try to get around it by claiming the circuit is, or could
be, for some appliance that exceeds 1440 VA (where that "appliance" may be
a UPS that subsequently supplies the computer(s)).
Finding proper surge protectors might be an issue. In theory I could use
German standard equipment because I think surge protection does not care
(much) about the frequency (e.g. 50 Hz vs. 60 Hz). Certainly it would
care about the voltage, and this would be quite different between Germany
and the US when looking at voltages relative to ground (where surges would
presumably be shunted), making such protection substantially less effective.
A side question: Given that grounded plugs are reversible in Germany, do
surge protection devices protect both power conductors with redundant parts
or are the devices designed to require that the plug only be inserted one
way (I've heard some UPSes require this and won't start if the plug is in
the opposite way).
There's virtually no market for 240V wiring in the USA. Special circuits
have to be installed to get that voltage and it won't be commonplace to get
them already in place unless many appliances use it. But the appliances
won't be made because almost no one can use them due to lack of circuits.
That much is a common problem in deploying something new. The NEC rule is
also in the way, and that probably needs to be changed before any of this
can be possible.
Under the concept of energy efficiency, many jurisdictions in the USA are
now pushing toward more energy efficient lighting like fluorescent lights.
Unlike incandescent, these lights actually work better on higher voltages.
There is also the NEC rule 210.6(A)(1) that blocks this. That one I think
should be rephrased to apply to incandescent only. Inductive ballasts do
come in multi voltage (separate wires per voltage). I presume electronic
ballasts can be autoranging and handle anything up to 277 volts easily.
Probably the biggest issue in enabling more use of higher voltage in the
USA is the variation. Some homes have 240 volts while a few (typically
apartments and condos in large buildings) only have 208 volts. But at
least this can still be handled by the few types of loads being considered
for this (e.g. fluorescent lights with autoranging ballasts and computers
with dual voltage or autoranging power supplies). The costs of switches
for the fluorescent lights would be higher due to the need to switch both
current carrying conductors, but once in mass production, they should be
less of a cost increase than the up front costs of changing incandescent
to fluorescent.
One side benefit of this is that more common availability of US style 240
volt circuits would reduce the need for special circuits under Article 647
of the NEC (these are the balanced power circuits with 60 volts between
hot and ground and 120 volts between both hots). A lot of audio equipment
now comes capable of international voltages these days.
just how much power it seems to be wasting (presumably as heat as opposed
to some other means like microwave radiation or flashing lights). It had a
listing with two voltage ranges, 100V-127V at 11.6A and 200V-240V at 4.8A.
I've seen several other power supplies, mostly from online tech specs, that
either show some level of increased efficiency at the higher voltage(s), or
at least no difference. Or is this really efficiency? Perhaps could it be
the case that it simply can provide a little more current on the DC side
when operated from the higher voltage? Any possibility that it's really a
frequency issue (e.g. more efficient at 50 Hz for some reason)?
I really think this is increased efficiency at higher voltage due to higher
currents at the lower voltage causing more heating. The few samples I have
seen don't really give me a good sense of how widespread this is, and how
much is lost over all power supplies on average. Anyone else have any real
figures for this?
The National Electrical Code used in the USA has a restriction 210.6(A)(2)
that limits the voltage between conductors to 120V for circuits supplying
cord-and-plug connected loads using 1440V or less, in dwelling units. This
a restriction I would like to see removed, or at least made substantially
lower, so that people in the USA can have circuits to power computers that
can run at a higher voltage for more efficiency, if they choose to do so.
Otherwise people wanting to do this would have to either violate the rule,
or be clever and try to get around it by claiming the circuit is, or could
be, for some appliance that exceeds 1440 VA (where that "appliance" may be
a UPS that subsequently supplies the computer(s)).
Finding proper surge protectors might be an issue. In theory I could use
German standard equipment because I think surge protection does not care
(much) about the frequency (e.g. 50 Hz vs. 60 Hz). Certainly it would
care about the voltage, and this would be quite different between Germany
and the US when looking at voltages relative to ground (where surges would
presumably be shunted), making such protection substantially less effective.
A side question: Given that grounded plugs are reversible in Germany, do
surge protection devices protect both power conductors with redundant parts
or are the devices designed to require that the plug only be inserted one
way (I've heard some UPSes require this and won't start if the plug is in
the opposite way).
There's virtually no market for 240V wiring in the USA. Special circuits
have to be installed to get that voltage and it won't be commonplace to get
them already in place unless many appliances use it. But the appliances
won't be made because almost no one can use them due to lack of circuits.
That much is a common problem in deploying something new. The NEC rule is
also in the way, and that probably needs to be changed before any of this
can be possible.
Under the concept of energy efficiency, many jurisdictions in the USA are
now pushing toward more energy efficient lighting like fluorescent lights.
Unlike incandescent, these lights actually work better on higher voltages.
There is also the NEC rule 210.6(A)(1) that blocks this. That one I think
should be rephrased to apply to incandescent only. Inductive ballasts do
come in multi voltage (separate wires per voltage). I presume electronic
ballasts can be autoranging and handle anything up to 277 volts easily.
Probably the biggest issue in enabling more use of higher voltage in the
USA is the variation. Some homes have 240 volts while a few (typically
apartments and condos in large buildings) only have 208 volts. But at
least this can still be handled by the few types of loads being considered
for this (e.g. fluorescent lights with autoranging ballasts and computers
with dual voltage or autoranging power supplies). The costs of switches
for the fluorescent lights would be higher due to the need to switch both
current carrying conductors, but once in mass production, they should be
less of a cost increase than the up front costs of changing incandescent
to fluorescent.
One side benefit of this is that more common availability of US style 240
volt circuits would reduce the need for special circuits under Article 647
of the NEC (these are the balanced power circuits with 60 volts between
hot and ground and 120 volts between both hots). A lot of audio equipment
now comes capable of international voltages these days.