2 Q:
Question 1:
Servicing Carrier Heat Pump 25HNA624 0030020.
Infinity thermostat displayed system "malfunction" needs service.
Trouble Codes: (all specific to 25HNA6) 75, 76, 77, 78 -- all related to "start voltage not achieved"
Not all together. Typically showing 75, 76 one day and 77, 78 another.
Cleaned out electrical compartment with compressed air.
The relay contacts show "camo type" discoloration. No evident pitting.
After blowing out the dirt and cobwebs in the electric compartment, the system is no longer identifying a malfunction and is running "normally".
Normal except that there are still intermittent days that trouble codes are being registered.
So I think the relays are on borrowed time.
From what I read on the site, relays are not cleaned but replaced but ...
- Is there a recommended spray cleaner to use on the relay contacts to extend life between replacing them? Or is a wear cycle a wear cycle and has nothing to do with outside cleanliness conditions?
What I have available locally is 'CRC Electronic Cleaner'.
--------------------------------------
ALSO-
Question 2:
Looking at replacement parts there are obvious physical differences though operation specs look the same. Some reference back to my equipment and some don't.
The existing spec is:
#3100-15Q228 HN51KC024
VAC ------FLA --LRA -RES------Coil 24VAC
-------------------------------------50/60 HZ
240/277----30--150---40
480---------30---75----40
600---------30---50----40
... for which my understanding is the 240/277 line applies to this residential equipment.
White Rodgers makes a mfg# 94-388
VAC -------FLA--LRA -RES-----Coil 24VAC
-------------------------------------50/60 HZ
277---------30--150----40
480---------30--125----40
600---------30--100----40
Can someone pat me on the head and confirm compatibility from that info?
Question 1:
Servicing Carrier Heat Pump 25HNA624 0030020.
Infinity thermostat displayed system "malfunction" needs service.
Trouble Codes: (all specific to 25HNA6) 75, 76, 77, 78 -- all related to "start voltage not achieved"
Not all together. Typically showing 75, 76 one day and 77, 78 another.
Cleaned out electrical compartment with compressed air.
The relay contacts show "camo type" discoloration. No evident pitting.
After blowing out the dirt and cobwebs in the electric compartment, the system is no longer identifying a malfunction and is running "normally".
Normal except that there are still intermittent days that trouble codes are being registered.
So I think the relays are on borrowed time.
From what I read on the site, relays are not cleaned but replaced but ...
- Is there a recommended spray cleaner to use on the relay contacts to extend life between replacing them? Or is a wear cycle a wear cycle and has nothing to do with outside cleanliness conditions?
What I have available locally is 'CRC Electronic Cleaner'.
--------------------------------------
ALSO-
Question 2:
Looking at replacement parts there are obvious physical differences though operation specs look the same. Some reference back to my equipment and some don't.
The existing spec is:
#3100-15Q228 HN51KC024
VAC ------FLA --LRA -RES------Coil 24VAC
-------------------------------------50/60 HZ
240/277----30--150---40
480---------30---75----40
600---------30---50----40
... for which my understanding is the 240/277 line applies to this residential equipment.
White Rodgers makes a mfg# 94-388
VAC -------FLA--LRA -RES-----Coil 24VAC
-------------------------------------50/60 HZ
277---------30--150----40
480---------30--125----40
600---------30--100----40
Can someone pat me on the head and confirm compatibility from that info?