Mark said:
Well, I've decided to go with 120VAC out to the camera and will tackle that
this weekend. I already purchased the romex that was on sale - $59 for 500'
of 12/2 which was pretty good IMO. I'm not going to dig a trench. Rather,
I'll be using 1/2" electrical pvc conduit running through heavy woods and will
shallow burry it before it enters the house.
I hate to burst your bubble, but before you do it, at least understand
that that installation will not comply with the electrical code. Table
300.5
in the 2002 NEC requires a minimum of 18" burial for your installation.
You could reduce that to 12" and be code compliant if you feed it
from a GFCI.
Personally, I would not do it. I'd look into a solar/battery source to
power the camera, or a time slicing arrangement, where the camera
draws power for rapid but brief intervals. Say you set it up to be on
1/10 of the time - 9/10 of the time the (low voltage) power from the
house charges the battery. So as an example, the camera turns on
once each tenth of a second for 1/100 of a second. I have no idea
what the time slices should be for your camera, but it seems worth
investigating. You would not need a lot of current to keep a battery
charged that way. In ten hours, with the camera drawing 1.5 amps
each time it turned on, you would use 1.5 AmpHours. In the same
ten hours, you would have 9 hours of charge time. If you charged
at .2 amps, that's 1.8 AmpHours - about the right amount. Your
500 foot run of romex would drop about .6 volts. An 18 volt supply
at the house feeding a charge circuit at the camera would work. In
addition, there is a built in "extra charge" period in daylight when the
camera doesn't use the LEDS and consumes a lot less. The issue in
doubt is whether your camera will work well at the time slice mentioned.