I am considering various backup options for my currently single sump
pump. One option is to use my old 1/3 HP sump pump (which I replaced
with a Zoeller M137 1/2 HP pump) and an inverter to run it, using a
12v relay to turn the inverter on.

My thinking is that a 1/3 HP rated pump probably uses about 4A of 120v
current. That translates to about 50A of 12v current (given the losses
etc).

i
 
E

Eric

Jan 1, 1970
0
Ignoramus1648 said:
I am considering various backup options for my currently single sump
pump. One option is to use my old 1/3 HP sump pump (which I replaced
with a Zoeller M137 1/2 HP pump) and an inverter to run it, using a
12v relay to turn the inverter on.

My thinking is that a 1/3 HP rated pump probably uses about 4A of 120v
current. That translates to about 50A of 12v current (given the losses
etc).

i
probably uses? Read the nameplate, its on there. Then you also need to allow
for starting surge which can be as high as 6 times full load, again see the
nameplate and look up "motor class".
Eric
 
G

George Ghio

Jan 1, 1970
0
Eric said:
probably uses? Read the nameplate, its on there. Then you also need to allow
for starting surge which can be as high as 6 times full load, again see the
nameplate and look up "motor class".
Eric
Better make that 10 times. Pumps start under load.
 