OT Coleman PowerMate Generator

A

amdx

Jan 1, 1970
0
I bought a Coleman PowerMate Generator (ProGen 5000) about 3 years ago.
Saturday evening about 5:00pm the power went out. The power co.
arrived about 7:00pm spent an hour testing and said "I think the problem is
a bad transformer." He left the scene.
I have several freezers that I needed to keep frozen. I pulled out the
still unopened generator box and put the wheels, feet and handle on the
generator. I put oil in the engine and went to get gasoline. (The price of
gas really sunk in when 2- two gal cans cost me $16.00)
I started the generator, plugged in all the freezers and noted indicator
lights were on. I logged all the temperatures and noted after about an hour
and 15 minutes all temperatures were lower than originally noted.
Everything was working as it should.
During all this time we had missed supper so went down the road for a bite
to eat. We returned within 45 minutes, the generator engine was running but
I had no indicator lights working. Somewhere around 10:30pm the current
stopped flowing. The circuit breaker had not tripped.
The power company was back with a crane and transformer, they installed it
and power came back on at 12:00am. They did good!
All the food is fine.
Today I called Coleman PowerMate and the recording said they have no
services rep available at this time. I thought maybe they weren't open yet
so I waited an hour and called again, same message.
I checked the internet, The company is closed, employees have been laid
off. http://igeneratepower.com/archives/30print/

They are being sued for overrepresenting specifications and service
problems.
http://www.bsdlaw.com/Investigations/Powermate.htm

Hope you had a better weekend.
Mike

PS. Sunday I found out my brother-in-law bought the same unit, his only
worked a short time also. He bought a Honda.
 
J

Jim Yanik

Jan 1, 1970
0
I bought a Coleman PowerMate Generator (ProGen 5000) about 3 years
ago. Saturday evening about 5:00pm the power went out. The power co.
arrived about 7:00pm spent an hour testing and said "I think the
problem is a bad transformer." He left the scene.
I have several freezers that I needed to keep frozen. I pulled out
the
still unopened generator box and put the wheels, feet and handle on
the generator. I put oil in the engine and went to get gasoline. (The
price of gas really sunk in when 2- two gal cans cost me $16.00)
I started the generator, plugged in all the freezers and noted
indicator
lights were on. I logged all the temperatures and noted after about an
hour and 15 minutes all temperatures were lower than originally noted.
Everything was working as it should.
During all this time we had missed supper so went down the road for a
bite
to eat. We returned within 45 minutes, the generator engine was
running but I had no indicator lights working. Somewhere around
10:30pm the current stopped flowing. The circuit breaker had not
tripped.

wonder if it was an infant failure?
perhaps in the field energizing circuit.ISTR some folks on alt.home.repair
discussing failed portable generators and that being a problem. It may be a
simple fix.
The power company was back with a crane and transformer, they
installed it
and power came back on at 12:00am. They did good!
All the food is fine.
Today I called Coleman PowerMate and the recording said they have no
services rep available at this time. I thought maybe they weren't open
yet so I waited an hour and called again, same message.
I checked the internet, The company is closed, employees have been
laid
off. http://igeneratepower.com/archives/30print/

They are being sued for overrepresenting specifications and service
problems.
http://www.bsdlaw.com/Investigations/Powermate.htm

Hope you had a better weekend.
Mike

PS. Sunday I found out my brother-in-law bought the same unit, his
only worked a short time also. He bought a Honda.

you have SEVERAL freezers?


What do you do during storm season? Perhaps you should buy a whole-house
generator,run on nat.gas or propane.
 
G

GregS

Jan 1, 1970
0
I bought a Coleman PowerMate Generator (ProGen 5000) about 3 years ago.
Saturday evening about 5:00pm the power went out. The power co.
arrived about 7:00pm spent an hour testing and said "I think the problem is
a bad transformer." He left the scene.
I have several freezers that I needed to keep frozen. I pulled out the
still unopened generator box and put the wheels, feet and handle on the
generator. I put oil in the engine and went to get gasoline. (The price of
gas really sunk in when 2- two gal cans cost me $16.00)
I started the generator, plugged in all the freezers and noted indicator
lights were on. I logged all the temperatures and noted after about an hour
and 15 minutes all temperatures were lower than originally noted.
Everything was working as it should.
During all this time we had missed supper so went down the road for a bite
to eat. We returned within 45 minutes, the generator engine was running but
I had no indicator lights working. Somewhere around 10:30pm the current
stopped flowing. The circuit breaker had not tripped.
The power company was back with a crane and transformer, they installed it
and power came back on at 12:00am. They did good!
All the food is fine.
Today I called Coleman PowerMate and the recording said they have no
services rep available at this time. I thought maybe they weren't open yet
so I waited an hour and called again, same message.
I checked the internet, The company is closed, employees have been laid
off. http://igeneratepower.com/archives/30print/

They are being sued for overrepresenting specifications and service
problems.
http://www.bsdlaw.com/Investigations/Powermate.htm

Hope you had a better weekend.
Mike

PS. Sunday I found out my brother-in-law bought the same unit, his only
worked a short time also. He bought a Honda.

You need about 4 K watts per fridg to get good reliable starting cuurent.
You would have had to start each device in sequence for a small generator
like that to run several freezers.

greg
 
A

amdx

Jan 1, 1970
0
wonder if it was an infant failure?
perhaps in the field energizing circuit.ISTR some folks on alt.home.repair
discussing failed portable generators and that being a problem. It may be
a
simple fix.
Thanks. Jim,
The manual does have a procedure to perform if there is a loss of residual
remagnetism. I may be wrong but it seems to me if the unit produced power
for an hour and was never shut down it would not lose its residual
magnetism. What ya think?
Thanks for the tip on alt.home.repair.
Mike
 
R

RFI-EMI-GUY

Jan 1, 1970
0
amdx said:
Thanks. Jim,
The manual does have a procedure to perform if there is a loss of residual
remagnetism. I may be wrong but it seems to me if the unit produced power
for an hour and was never shut down it would not lose its residual
magnetism. What ya think?
Thanks for the tip on alt.home.repair.
Mike
I would guess that since it had just been used the first time, that a
loose wire vibrated off somewhere between the generator and the output
jacks.

--
Joe Leikhim K4SAT
"The RFI-EMI-GUY"©

"Treason doth never prosper: what's the reason?
For if it prosper, none dare call it treason."

"Follow The Money" ;-P
 
A

amdx

Jan 1, 1970
0
RFI-EMI-GUY said:
I would guess that since it had just been used the first time, that a
loose wire vibrated off somewhere between the generator and the output
jacks.
I did an external check, didn't see any problem. I'll pull a cover and look
inside.
Thanks, Mike
 
A

amdx

Jan 1, 1970
0
I bought a Coleman PowerMate Generator (ProGen 5000) about 3 yearssnip, snip.

Ok, I went out and checked connections, looked good. I got out a 12v power
supply and connected it per the manual to remagnetize the unit. I heard the
motor drag down, plugged in a light and it is producing power.
With a small 50 watt load the output voltage is only 104 Volts.
I came in wrote the post, then decided to try a bigger load. The unit had
lost its magnetism. I remagnitized it and connected an 1800 watt load and
the output voltage is only 94 volts.
Doesn't seem good!
Mike
 
A

amdx

Jan 1, 1970
0
BobW said:
Mike,

I bought a Honda EM2500X after the Northridge earthquake in 1994 (I had to
wait for the shaking to stop). I hadn't used it since then and foolishly
didn't treat the gas and didn't keep it full of gas.

A few weeks ago, I decided to get it running. I assumed the carburetor and
gas tank needed attention and I didn't even attempt to start it. So, I
cleaned the caburetor and the gas tank (a simple job). It fired on the
first pull and runs a 1200 watt heat gun with almost no drop in output
voltage.

The Honda's do cost a little more than others. Now, I know why.

Bob
--
My hindsight is almost 20-20. :)
Mike
 
A

amdx

Jan 1, 1970
0
Tim Wescott said:
It sounds like whatever should be powering the field coil isn't. Whatever
circuit you were attaching that 12V to is the circuit that's haywire.
Chances are even that it lost a connection (as suggested) or, since this
brand seems to suffer from infant mortality, that some design defect in
the field control circuit has made it blow a part.
Tim Wescott

Thanks Tim,
I'll try to find some general info (if I can't find specific to this
generator) on ac generators and see what the field drive circuit looks like.
I read one posting about two defective diodes in one mans generator.
 
J

Joerg

Jan 1, 1970
0
amdx wrote:

snip, snip, chop, thwack, stomp, stomp, stomp.

SCNR :)
Ok, I went out and checked connections, looked good. I got out a 12v power
supply and connected it per the manual to remagnetize the unit. I heard the
motor drag down, plugged in a light and it is producing power.
With a small 50 watt load the output voltage is only 104 Volts.
I came in wrote the post, then decided to try a bigger load. The unit had
lost its magnetism. I remagnitized it and connected an 1800 watt load and
the output voltage is only 94 volts.
Doesn't seem good!


It sure doesn't sound good. I don't know this generator but if this one
has a DC voltage applied to slip rings then that is often used to
regulate the output. So if this regulator went bad the generator may
become unregulated and eventually lose residual field.
 
R

RFI-EMI-GUY

Jan 1, 1970
0
RST said:
Come on, fellers, learn to snip.

Jim


Thats the problem with bottom posting!

--
Joe Leikhim K4SAT
"The RFI-EMI-GUY"©

"Treason doth never prosper: what's the reason?
For if it prosper, none dare call it treason."

"Follow The Money" ;-P
 
A

amdx

Jan 1, 1970
0
You need about 4 K watts per fridg to get good reliable starting cuurent.
You would have had to start each device in sequence for a small generator
like that to run several freezers.

greg
Greg, that may be fine in theory, but, I ran 6 freezers, all of them
started, all of them
ran and all of them had a 4 to 7 degree temperature drop in the hour that
they ran.
I have individual thermometers on each freezer. Four of these frezers are
newer Kenmore freezers if that means anything. Luckily they were all set
between -4F
and -12F when the power went out. One old freezer got up to 12F, the new
ones only rose to 7F.
Mike
 
J

Jim Yanik

Jan 1, 1970
0
Thanks Tim,
I'll try to find some general info (if I can't find specific to this
generator) on ac generators and see what the field drive circuit looks
like. I read one posting about two defective diodes in one mans
generator.

those diodes must be in the DC outlet section,as AC generators don't need
diodes for AC output.

The 94V output is a clue to the failure;you are generating voltage under
load,but low. I'd say the field coil is not being energized sufficiently.

maybe one section of the field coils opened,perhaps a bad solder joint.
 
J

Jim Yanik

Jan 1, 1970
0
Greg, that may be fine in theory, but, I ran 6 freezers, all of them
started, all of them
ran and all of them had a 4 to 7 degree temperature drop in the hour
that they ran.
I have individual thermometers on each freezer. Four of these
frezers are
newer Kenmore freezers if that means anything. Luckily they were all
set between -4F
and -12F when the power went out. One old freezer got up to 12F, the
new ones only rose to 7F.
Mike

WHAT do you use SIX freezers for? Waiting for the big disaster?
You've aroused my curiosity.
 
A

amdx

Jan 1, 1970
0
Tim Wescott said:
That's where I was going, although I'm also suspecting the field current
control circuit.

The inexpensive way to design such a generator would be to rectify the
120V AC for the field coil, or have an auxiliary AC output winding that
gets rectified; bad diodes in that rectifier would render the field
circuit useless.
I've located a pictorial on the Coleman site, it has a bridge diode and a
capacitor.
I'll have a look in the next few days.
Mike
 
J

Jim Yanik

Jan 1, 1970
0
That's where I was going, although I'm also suspecting the field
current control circuit.

The inexpensive way to design such a generator would be to rectify the
120V AC for the field coil, or have an auxiliary AC output winding
that gets rectified; bad diodes in that rectifier would render the
field circuit useless.

I was thinking the field coil is several small coils on the rotor,the
stator coils being the AC output,thus no slip rings and brushes needed for
the high current output.
A bad solder joint or broken wire on one rotor (field) coil would reduce
but not eliminate the AC output.

It might be interesting to scope the AC output,see what the output waveform
looks like.
 
A

amdx

Jan 1, 1970
0
RFI-EMI-GUY said:
Thats the problem with bottom posting!
I agree with you Joe,
I would prefer top posting, When I go through a thread it's a constant to
have to page down through all the stuff you have already read. I'm still
looking for a program that would open a post and automatically page down to
the bottom of that post.
Mike
 
A

amdx

Jan 1, 1970
0
Jim Yanik said:
WHAT do you use SIX freezers for? Waiting for the big disaster?
You've aroused my curiosity.
Its business use.
Mike
 