PIC and 10-Bit ADC
Okay something again I need to wrap my head around.
My PIC datasheet says that it reads the 10-bits from a 16-bit analog
register based on the analog input.
ADRESH takes the first 10-bits, and ADRESL takes the last 10-bits.
If my input voltage is say 2.564 volts, what would be the ADRESH and
ADRESL, barring any binary conversion.
I know that I have to divide 5/256 to get 20ma increments that are
detectable.
But am I going to get the actual 2.564 fully read in to either of these
registers, or am I going to lose some info if I take the wrong 10-bits?
Anthony Fremont
Please tell me what document told you this. A PIC model number would
also be helpful to us. Since you didn't specify one, I will pick the
16F88.
Hardly. ADRESH and ADRESL are only 8 bits each in size. The 10 bit
result can be left justified or right justified depending upon another
SFR bit setting. The ADFM bit in the ADCON1 register determines whether
the result will be left or right justified accross the two ADRESx
registers.
We would need to know what you are using for Vref to tell you that.
Assuming that you are using a 5V Vcc as your Vref then each increment
would correspond to (5/1024) or about 4.88mV.
detectable.
10-bits?
Again, the registers are only 8 bits in size. That's why there are two
of them. To achieve 10 bit precision you will need the data from each
register. If you only want an 8 bit result (giving 4.88mV * 4 or about
19.53mV per increment) then specify left justification by clearing the
ADFM bit in ADCON1, take the value of ADRESH and ignore what's in
ADRESL.
John Popelish
Actually, I think you can choose left justified (upper 8 bits in
ADRESH, lower 2 bits in high end of ADRESL, others zeroed) or right
justified (high two bits in low end of ADRESH, others zeroed, lower 8
bits in ADRESL)
2.564 out of 5 with a 10 bit resolution is (2.564/5)*1023 = 525
(rounded to the nearest integer) decimal or 1000001101 binary.
If set up for left justified, ADRESH would hold the left 8 bits of
that, or 10000011 and ADRESL would hold the right two bits in its left
end with the rest filled with zeros, or 01000000.
If set up for right justified, ADRESH would hold the left 2 bits of
that value in its right end, with the left bits filled with zeros, or
00000010 and ADRESL would hold the right 10 bits or 00001101.
If you just want the voltage measured using the most significant 8
bits and intend to waste the lower two bits, use left justification
and take ADRESH as the result. If you intend to do treat the result
as a 10 bit binary value that fits in a 16 bit space, (for instance,
if you intend to do some 16 bit math on it to perform digital
filtering) you use right justification and both registers.
detectable.
If you use left justification and the ADRESH value as an 8 bit
conversion (0 to 255 range), each count in ADRESH represents 5 volts
divided by 255 or .01961 volts. If you use right justification and
use both resistors to measure the voltage as a 16 bit number (with
only 10 of those bits ever used, each count represents a voltage of
5/1023 or .00489 volts. But your program will have to make magnitude
decisions based on two byte programming, so each value comparison will
be a little more complicated.
Anthony Fremont
AIUI the divisor to use is 256.
1024 :)
John Popelish
There are 256 possible voltages to be measured, but one of them is
zero, so the range is divided by 2^8-1.
One less, for the same reason. 1024 end points, but only 1023 spaces
between them.
Anthony Fremont
between them.
Assuming a Vref of 4.096V and an "ideal" 10 bit ADC to make things
simple, a conversion result of 0 would actually encompass the range of
0V-.00399R Volts; the second range for a reading of 1 is .004V to
..00799R Volts. Consequently the final range would be for (1023*.004)
4.092V thru 4.096V. Is that not correct?
John Popelish
The way I see it, each level is ideally converted with an accuracy of
+,- 1/2 LSB, except for the first and last level. 0 is converted to
an accuracy of -0, +1/2 LSB and the highest level is converted to an
accuracy of -1/2LSB to +0.
Anthony Fremont
I can't find any mention of excepting the first and last levels in the
datasheet nor in the mid-range reference manual. I can't help but
wonder why precision voltage references obviously assume 2(n) steps and
not 2(n)-1. FWIW, my John Peatman book seems to agree with me. Perhaps
an ADC expert could shed some light on this?
Bob Monsen
Why is the last level (255) only representing a range up to Vref - 1/2
LSB? Given your analysis, it only gets within 1/2 LSB of Vref. To me, that
means you have an extra 1/2 LSB left over to explain... ;)
However, if you assume that the output is based on the floor of the
range (which I believe is the case) then everything works out properly:
0*Vref/256 to 1*Vref/256 -> 0,
1*Vref/256 to 2*Vref/256 -> 1,
2*Vref/256 to 3*Vref/256 -> 2,
255*Vref/256 to 256*Vref/256 -> 255.
Unless I'm miscounting, that means you have 256 voltage ranges, which map
neatly to the 256 values that your 8 bit ADC output can take on.
OTOH, the difference between 1/255 and 1/256 is so small that this
will make absolutely no difference for most situations, except that you
won't be able to use shifts to do the math.
Regards,
Bob Monsen
We should take care not to make the intellect our god; it has, of
course, powerful muscles, but no personality.
Albert Einstein
John Popelish
I think I have made a mistake about the voltage per step being 1/2^n-1
times the full scale voltage, because that conflicts with the first
and last levels being at 1/2 LSB value. But I think it is true that
the first and last step are 1/2 LSB, while all the others are 1 LSB
wide. Here is an excerpt from a National data sheet for an 8 bit
successive approximation A/D converter:
http://cache.national.com/ds/DC/ADC081S101.pdf
(begin excerpt)
Code transitions occur midway between successive integer
LSB values. The LSB width for the ADC081S101 is VA/256.
The ideal transfer characteristic is shown in Figure 5. The
transition from an output code of 0000 0000 to a code of
0000 0001 is at 1/2 LSB, or a voltage of VA/512. Other code
transitions occur at steps of one LSB.
(end excerpt)
Unfortunately, the voltage versus count diagram immediately following
does not reflect this paragraph.
However, I have seen others that do.
For instance, all the voltage versus count graphs in this Maxim
application note show the first step as 1/2 LSB and all the rest as 1 LSB.
http://www.maxim-ic.com/appnotes.cfm/appnote_number/748
John Popelish
Here is another reference that mentions both the first and last step
being only 1/2 LSB and the voltage per step (1 LSB) being (1/2^n -1)*Vref:
http://focus.ti.com/lit/an/slaa013/slaa013.pdf
(begin excerpt)
The width of one step is defined as 1 LSB (one least significant bit)
and this is often used as the reference unit for other
quantities in the specification. It is also a measure of the
resolution of the converter since it defines the number of
divisions or units of the full analog range. Hence, 1/2 LSB represents
an analog quantity equal to one half of the analog
resolution.
The resolution of an ADC is usually expressed as the number of bits in
its digital output code. For example, an ADC
with an n-bit resolution has 2n possible digital codes which define 2n
step levels. However, since the first (zero) step
and the last step are only one half of a full width, the full-scale
range (FSR) is divided into 2n – 1 step widths.
Hence
1 LSB = FSR/(2^n - 1) for an n bit converter.
(end excerpt)
Bob Monsen
(begin excerpt)
resolution.
range (FSR) is divided into 2^n - 1 step widths.
Hence
(end excerpt)
You appear to be right about the first transition starting at 1/2 LSB
after 0. This makes the jagged line on the graph of voltage vs values have
a smaller difference between the 'theoretical' line, thus making the
digitization error smaller.
However, they are wrong about that divisor, at least for some ADC chips.
It is pretty confusing, I'll agree, but if you just make yourself a graph
of input voltage vs output codes, you see that the last value represents
3/2 LSB. (This is also pointed out in an Analog Devices datasheet for the
AD9226, page 7 and 19.)
The voltage is exactly represented at the midpoint of each step, so there
is a possible error for each bit of up to +- 1/2 LSB. Now, imagine a 2 bit
converter (so to speak...) that uses a FS Vref of 1V. It'll have
output transitions at 1/8, 3/8, and 5/8V. That means that for an output
value of 1, the input voltage was 1/4 +- 1/8. For an output value of 0,
the input voltage was 0 +- 1/8. etc. So, the input voltage is within 1/2
LSB (1/8V) of output/4.
The AD9226 actually considers input voltages that are greater than -1/2LSB
to be valid inputs, and considers input voltages above FS - 1/2LSB to be
*invalid*. The out of range output pins are defined this way.
However, it is possible that the scale is stretched on other converters.
If the scale is stretched, then for those converters, the LSB may actually
be as you say. For our 2-bit converter, that would make transitions at
1/6, 3/6, and 5/6. This would result in a maximum error of 166mV as
opposed to 125mV with the other encoding scheme, and thus a bigger
encoding error.
Regards,
Bob Monsen
Albert Einstein
Anthony Fremont
That's roughtly the way I see it. The only thing I would change is that
your numbers are a little bit ambiguous in that you allow one voltage to
return two different values. That's why I went with the 999R thingy.
It seems to me that precision (.1%) voltage references indicate that
2(n) is the appropriate divisor.
True, but we're being pedantic here. ;-) Besides, I really want to
know which is correct. With Google it's a split decision. Microchip
documentation seems to agree with 2(n), but others agree with John.
Regards,
Bob Monsen
Albert Einstein
Now there's somebody worth quoting. (;-)
Anthony Fremont
(begin excerpt)
resolution.
This all sounds simple/reasonable enough.
I'm with you so far. ;-)
Hence
(end excerpt)
I'm kinda dumb, so I don't really get how they arrive at that
completely. :-? I can see that it might be hard to acheive + or -
resolution at the extreme ends of the scale since you can't really be
less than 0 or greater than Vref so that would seem to remove half of
its range, making the first and last steps half-width.
The Peatman books show a stair-case with input voltage on the horizontal
scale and the ADRES value vertically. The first step is flat (ADRES =
0) for a full step width. The last step peaks early in the way that I
described (returning 0x3FF for a voltage less than Vref. Next time I'm
tinkering with the PIC ADC, I'll do some measurements to see where the
first (0x00 -> 0x01) and last (0x3FE -> 0x3FF) transitions occur. It
should prove kinda interesting to see if the first transition occurs at
2mV (4.096 reference).
Bob Monsen
I think it depends on the converter. I bet some do it one way, and others
do it the other way. It is an arbitrary choice. One way gives you more
steps, and thus less quantization error, while the other way gives you a
larger usable range.
Regards,
Bob Monsen
Imagination is more important than knowledge...
Albert Einstein
John Popelish
Yes, we should pick a particular A/D and nail that one down, first.
Then we will be in a position to look for exceptions.
John Popelish
Bob said:
I looked, but it doesn't make sense to me. The -FS and +FS ends of
the scale are not symmetrical, with the lowest output transition
taking place at (-FS) +1/2LSB, but the highest transition taking place
at (+FS) -1 1/2 LSB, which can't be correct. Can it? Is there any
A/D data sheet that gets everything correct? No wonder there is
disagreement on how these things work.
Pooh Bear
It's been jolly interesting following you guys discussing this.
I rather think you left the OP at the starting line though ! ;-)
Graham
John Popelish
You'll have that, sometimes. I'm here on a generous impulse, but when
something comes along that serves my education, I have no problem
taking a detour. We spent quite a bit of effort explaining the left
and right justification modes and ranges of the O.P.'s A/D, before we
left him to explore this detail. And just because we are doing this,
you are certainly free to continue with the hand holding.