I read The following from: http://www.leminstruments.com/grounding_tutorial/html/soilresistivitytest.shtml
Measuring Soil Resistivity 4 - Pole Method
The calculation of this measurement can be simplified by converting distance in cm to distance in feet giving you the following equation:
p = 191.5AR
Where: p = the average soil resistivity to depth
in ohm - cm
A = the distance between electrodes in feet
R = the measured resistance value in ohms
from the test instrument
For example, you have decided to install 10' ground rods as part of your grounding system. To measure the soil resistivity at a depth of 10' requires that the spacing between the test electrodes is 10'. The depth that the test electrodes is to be driven is A/20.
Lo
ok at this"The depth that the test electrodes is to be driven is A/20."
then he said: The ground stakes are positioned in a straight line equidistant form one another and at a distance between one another reflecting the depth to be measured. The ground stakes should be screwed
in no deeper than 1/3 the distance from one another.
he confuse me A/20 or no more than 1/3 A
and in the figure he present (see below) he put
a and in formulas he use
A
please help me to understand it
thanks
View attachment 38108