DJ said:
www.nmsu.edu/~tdi/pdf-resources/cc68.pdf
The DC rating on a QO breaker is voltage specific, not like a
dedicated DC breaker. It *would* be better to use a purpose built DC
breaker in your DC disconnect box, for instance. Actually, they're
often alot cheaper than QOs are...
In that case, you're probably ok. Check your local code, of course.
Actually, make sure that your wiring will take 30 amps (~#10) because
the breaker is supposed to be the weak link in the circuit.
DJ
Thanks DJ
I got a email from the fine folks at Alter Systems and I am considering
going with the Outback PS2 DC Breaker box with 175 amp inverter breaker and
the GFI breaker installed.
Our city code requires NEC 2003 so a nice trip to the library to read up and
the supervision of a master electrician friend upon install shoud be
helpful.
Also I have been reading a pdf from Alternate Energy about solar power and
what would meet code and what would not. That was an eye opener.
I am going with the *would* be better as inspectors in this area might feel
more comfortable with dedicated home solar power equipment.
Thanks for the advice on #10 as I have #12 outdoor uv rated.
I can always use the QO box in the garage, It was wired in 1924. Time for an
upgrade.
I will look into replacing the Pushmatic panel and several good condition
post and wire circuits in the house.
There have been about 4 upgrades to the wiring in the past but nobody went
to the bother of doing a full job.
Again thanks for everyones help, I will let you all know how it turns out.
Randy