I am guessing that ‘M/C’ means Motor Control.
It also sounds like you are dealing with 3 phase
Power so the motor control you are talking about
Must be a fairly hefty one.
What concerns me is not the 30A rating of
The controller but the current demand of the
Motors you plan on using. At 220V with 7A
You can expect around 3-4 Hp or 1500W
(Note: I just rounded, I did not compensate for
3 phases or power balancing)
If the motor is under that range then you should not have a problem
The transformer can only provide up to 14 amps max, and if the
Motors only draw 14A max then the 30 rating of the controller
Should be a blessing as it can easily handle the load.
The one thing that you did not make clear is the type of
Transformer you have. I am guessing you have a step down
Transformer to drop from 415 down to 220. I have not encountered
A large number of 3phase transformers that make such a small
Step. Usually I see 13,800V down to 220. I was worried that you
Had a single phase transformer and you wanted to get 3 phase
Power from it.