What are the effects of a leading power factor?

?

.

Jan 1, 1970
0
We have gone past unity, possibly leading by 10% - 20%
Is there any harm in this or should we be correcting it back to 90% to
100%? The plant contains mostly transformers and HID lights.
There are a few VSD motor starters but a very small proportion of the
load.

To send me e-mail remove the sevens
from my address.

Chrisd
 
L

Louis Bybee

Jan 1, 1970
0
. said:
We have gone past unity, possibly leading by 10% - 20%
Is there any harm in this or should we be correcting it back to 90% to
100%? The plant contains mostly transformers and HID lights.
There are a few VSD motor starters but a very small proportion of the
load.

To send me e-mail remove the sevens
from my address.

Chrisd

Please provide additional details such as:

What leads (pun unintended :-] ) you to believe you do in fact have a
leading power factor.

What instrumentation was used for quantification, and who was
operating/interpreting the resulting data?

What you describe is a rather unusual situation, and with the equipment
listed, unless there is equipment we are unaware of, the power factor should
be approximately what you list except lagging.

Louis
 
M

murgatroid

Jan 1, 1970
0
Power company charges your more or less depending upon your average PF,
Contact them, they like extra capacitive loading and will reduce your rates.
 
C

Charles Perry

Jan 1, 1970
0
murgatroid said:
Power company charges your more or less depending upon your average PF,
Contact them, they like extra capacitive loading and will reduce your rates.
Actually, depending on the tariff, you can pay MORE if you are leading. If
your penalby is based on a kVA charge, leading or lagging will get you the
same penalty. From the utilities viewpoint lagging is bad, leading is bad,
unity is good.

Charles Perry P.E.
 
S

sammmm

Jan 1, 1970
0
yes, it does hurt to go leading.
i've had customers complaining about blowing fuses, losing SCRs, heating
transformers, etc.
we pulled the billing for electric and found, even without metering, the
problem.
we disconnected some caps to get back to lagging and the problem
disappeared.
this happened at two different plants of unassociated companies.
sammmm
 
D

Don Kelly

Jan 1, 1970
0
Extra capacitive loading helps hold voltage up but any demand metering
doesn't give a damn as to whether you are leading or lagging. You might not
get any more than thanks if you are helping.
 
J

J. B. Wood

Jan 1, 1970
0
"Charles Perry" said:
Actually, depending on the tariff, you can pay MORE if you are leading. If
your penalby is based on a kVA charge, leading or lagging will get you the
same penalty. From the utilities viewpoint lagging is bad, leading is bad,
unity is good.

Charles Perry P.E.

Hello, and I've never heard of a kVA cost. Certainly in residential
service one pays only for the energy (kW-hrs) consumed. Your electric
bill is based upon energy usage (as indicated by the utility meter
reading) regardless of whether current and voltage are in phase or not.
The idea that a customer can somehow change the power factor and pay a
lower monthly bill is pure urban myth. Sincerely,

John Wood (Code 5550) e-mail: [email protected]
Naval Research Laboratory
4555 Overlook Avenue, SW
Washington, DC 20375-5337
 
C

Charles Perry

Jan 1, 1970
0
J. B. Wood said:
Hello, and I've never heard of a kVA cost. Certainly in residential
service one pays only for the energy (kW-hrs) consumed. Your electric
bill is based upon energy usage (as indicated by the utility meter
reading) regardless of whether current and voltage are in phase or not.
The idea that a customer can somehow change the power factor and pay a
lower monthly bill is pure urban myth. Sincerely,

John Wood (Code 5550) e-mail: [email protected]
Naval Research Laboratory
4555 Overlook Avenue, SW
Washington, DC 20375-5337

KVA (demand) charges are almost standard practice for industrial customers,
and are quite common for commercial tariffs also. Average pf, kvarh, etc
power factor penalties are common for commercial customers. For the most
part, only residential customers get a free ride with regard to power
factor. Tariffs for many utilities are available online. Look them up. Of
course, knowledge of metering practices and terminology will be necessary to
interpret them.

Charles Perry P.E
 
D

Don Kelly

Jan 1, 1970
0
| In article <[email protected]>, "Charles Perry"
|
|> |> > Power company charges your more or less depending upon your average PF,
|> > Contact them, they like extra capacitive loading and will reduce your
|> rates.
|> >
|> Actually, depending on the tariff, you can pay MORE if you are leading. If
|> your penalby is based on a kVA charge, leading or lagging will get you the
|> same penalty. From the utilities viewpoint lagging is bad, leading is bad,
|> unity is good.
|>
|> Charles Perry P.E.
|
| Hello, and I've never heard of a kVA cost. Certainly in residential
| service one pays only for the energy (kW-hrs) consumed. Your electric
| bill is based upon energy usage (as indicated by the utility meter
| reading) regardless of whether current and voltage are in phase or not.
| The idea that a customer can somehow change the power factor and pay a
| lower monthly bill is pure urban myth. Sincerely,

A given kVA at a power factor less than zero is less kW used. So not only
is it a myth, it is a non-usage. If your current phase angle is other than
0 degrees from the voltage phase angle, you're giving power back during at
least part of the cycle. So that's power you are not using. At 90 degrees
you're giving back all you take, so none can be used. At 180 degrees you're
running a generator.

The notion that you can cheat the power company with a bunch of capacitors
or inductors to swing the phase of your current angle fails simply because
you still end up with a real component equal to your real usage, regardless
of how much additional power gets sloshed around in your reactance. The
meter is still going to show the difference between what is coming and what
is going (if it's one that runs backwards on what is going).
http://ka9wgn.ham.org/ |
--------------------------------------------------------------------------
---

KVA demand charges do take into account power factor (by the way I believe
that tyou meant less than 1 not less than 0) The energy seen by a KWH meter
is unchanged as you indicate - except that, at any power factor except
unity the current, at a given voltage will be higher than the minimum
required to produce power. 1)the losses will be higher - customer pays more
in energy charges.
2)( and this is more important) the heating of the utilities transformers,
lines, generators, etc will be higher and such equipment must be sized on
the basis of KVA, not KW.
Poor power factor costs the utility (a 2.5 KW load at 0.5 pf is a 5KVA load
as seen by the transformer and it must be sized accordingly), and this cost
is passed on to the customer with such a poor power factor (or poor load
factor) in the form of demand charges based on KVA. This is not done for
residential customers as it is simply cheaper and easier to take into
account typical residential pf in the rate structure.
3) Poor pf -lagging- can cause excessive voltage drops. excessive leading
vars can also cause problems.

No myths, either urban or otherwise are involved- just economics.

It is then often advantageous for commercial and industrial customers to
provide some pf compensation - and this is done. Correction to exactly unity
pf is not done nor is it economic- There is an optimum point but few bother
with the calculation of such an optimum in design..
 
D

Don Kelly

Jan 1, 1970
0
That may be true- it was routinely done in the area that I used to live in.
Note that KVA demand metering was based on monthly peak where the meter had
a thermal(?) lag so that it rode through starting transients and short peaks
and represented what was important to the utility - temperature rises in
equipment.
--
Don Kelly
[email protected]
remove the urine to answer
s falke said:
Don Kelly said:
Extra capacitive loading helps hold voltage up but any demand metering
doesn't give a damn as to whether you are leading or lagging. You might not
get any more than thanks if you are helping.

Rumour has it that "true" KVA-demand metering [aside from residential] is
fairly well entrenched.above the 49th.

-s falke
 
J

J. B. Wood

Jan 1, 1970
0
No Spam said:
"I've never heard of it and don't understand it so it can't be."

What you are saying is true for residential customers, but not so
for industrial. I once changed the taps on a couple of
transformers feeding SCR rectifiers (5MW DC supplies) that were
running phased back and eliminated a $4000 / month kvar charge.

Well, Mr. "I do understand it and it can be", you are being redundant by
using the term "SCR rectifiers." Sincerely, and with jab intended,

John Wood (Code 5550) e-mail: [email protected]
Naval Research Laboratory
4555 Overlook Avenue, SW
Washington, DC 20375-5337
 
D

Don Kelly

Jan 1, 1970
0
| That may be true- it was routinely done in the area that I used to live in.
| Note that KVA demand metering was based on monthly peak where the meter had
| a thermal(?) lag so that it rode through starting transients and short peaks
| and represented what was important to the utility - temperature rises in
| equipment.

Sounds like exactly the right way to measure for the component of costs
that relates to purchasing, installing, and maintaining transmission and
distribution facilities.

So, given 2 customers that periodically have a 1000 kVAR demand, but run
regularly around 100 kW, where one of them has pf 0.97 and the other has
pf 0.66, how are they going to measure the added charges for the second?
A kVAR usage meter?
---
The meters measured kVA (not kVAR) demand and the needle pushed another
needle so that the peak kVA during the period is registered. Your two
customers would have the same kVA demand charge as both require the utility
to provide the same equipment capability but the first would have a higher
kWH bill as he uses more energy. The effective cost per kWH would be lower
for him than for the second person. Both are being charged for a high kVA
(not necessarily kVAR) peak demand because of a fluctuating load and the
second gets a whammy in this respect from poor pf. The KVA demand
penalises high peak (over 15 to 30 minutes duration) to average loads as
well as poor power factor.

Take another case - steady 100KVA loads - first one at 0.97 pf lag and the
second at 0.66 pf lag. Each pay $0.08 per KWH so that over the billing
period (say 720 hours) he will pay $5587 for energy and (at $2/KVA) $2000
for demand - total $7787 for $0.11 "average cost per KWH"
The second pays $2000 for the demand charge and $3802 for energy - "average
cost per KWH" becomes $0.13 per KWH. In this case it would be beneficial for
the second user to install capacitors.

Another case- first one 100KW steady at 1.0 pf and second 100KW steady at
0.66pf lag
First pays $200+5760=$5960 Second pays $303+7760 =$8063 for the same actual
energy used.

Third case: both at 100KW average- first as above and the second with a peak
of 1000kVA- both at unity pf. First pays $5960, second pays $7760

A demand charge based on KVA peaks which exist long enough for equipment to
reach a steady state operating temperature reflects both the effect of high
load peaks as well as poor power factor.
--
Don Kelly
[email protected]
remove the urine to answerhttp://ka9wgn.ham.org/ |
--------------------------------------------------------------------------
---
 
D

Don Kelly

Jan 1, 1970
0
| KVA demand charges do take into account power factor (by the way I believe
| that tyou meant less than 1 not less than 0) The energy seen by a KWH meter

Yes, I meant less than one. Sorry about that.

| is unchanged as you indicate - except that, at any power factor except
| unity the current, at a given voltage will be higher than the minimum
| required to produce power. 1)the losses will be higher - customer pays more
| in energy charges.

If your power factor is 1.0, you're not wasting any more power than in the
proportion to what you use, relative to the efficiency of the whole
system.
------------
I may not have been clear- at any pf other than unity -losses per unit of
useful energy are increased. Customer pays for the losses on his side of the
metering.
| 2)( and this is more important) the heating of the utilities transformers,
| lines, generators, etc will be higher and such equipment must be sized on
| the basis of KVA, not KW.

And of course this extra waste has two components. The facility cost to
scale it up to be able to slosh the power around for the customer's sloppy
load, and the energy lost while sloshing it around.


| Poor power factor costs the utility (a 2.5 KW load at 0.5 pf is a 5KVA load
| as seen by the transformer and it must be sized accordingly), and this cost
| is passed on to the customer with such a poor power factor (or poor load
| factor) in the form of demand charges based on KVA. This is not done for
| residential customers as it is simply cheaper and easier to take into
| account typical residential pf in the rate structure.

As long as the demand charges relate ONLY to physical facility capacity
costs, then that is the right thing to do. The loss of energy due to the
inefficiency (small percentage) in transmission and distribution should
also be paid for by the customer that insists on doing that, but it should
be based on actual usage; a demand figure doesn't measure this part.
--------
Demand metering doesn't replace energy metering- it is additional to the
energy metering. Demand metering doesn't measure efficiency or losses. All
that it indicates is the peak sustained kVA during a billing period.
Customer's inefficiencies will affect this peak and the loading of
transformers etc so, in that respect, the demand is affected correctly. The
customer pays directly for his losses in the energy charges (actual energy
use). In addition, losses in the utility system are not generally
attributable to a given customer so the overall energy rates include these
losses along with other operating costs, executive lunches, and investor
dividends.

--
Don Kelly
[email protected]
remove the urine to answer

. > | 3) Poor pf -lagging- can cause excessive voltage drops. excessive
leading
| vars can also cause problems.
|
| No myths, either urban or otherwise are involved- just economics.

I think the myth is that all one has to do is get their current and voltage
to be out of phase by 90 degrees relative to each other and the classic
home power meter won't measure it. To whoever believes that then I suggest
going all the way to 180 degrees and run the meter backwards so the power
company pays you to use their electricicty :)

Of course, none of that is real.


| It is then often advantageous for commercial and industrial customers to
| provide some pf compensation - and this is done. Correction to exactly unity
| pf is not done nor is it economic- There is an optimum point but few bother
| with the calculation of such an optimum in design..

The problems I run into in designing and build computer data centers is more
a harmonic issue. But even then there are phasing issues as many computer
power supplies have narrow current spikes and are thus not evenly distributed
over the AC cycle. One of the things I want to study is ways to balance such
large non-linear loads (100's to 1000's of computers) so that current peaks
do not get excessive (which can happen if all the power supplies work at the
same part of the cycle, which tends to be true). I've started putting some
thought into splitting things up into 6 or 12 phases. But then, that can
also create lower power factor, too. Maybe balancing just how many of the
various loads are sucking current at specific phase angles could approach
making it look linear and unity. ----
http://ka9wgn.ham.org/ |
--------------------------------------------------------------------------
---
 
D

daestrom

Jan 1, 1970
0
| The meters measured kVA (not kVAR) demand and the needle pushed another
| needle so that the peak kVA during the period is registered. Your two
| customers would have the same kVA demand charge as both require the utility
| to provide the same equipment capability but the first would have a higher
| kWH bill as he uses more energy. The effective cost per kWH would be lower
| for him than for the second person. Both are being charged for a high kVA
| (not necessarily kVAR) peak demand because of a fluctuating load and the
| second gets a whammy in this respect from poor pf. The KVA demand
| penalises high peak (over 15 to 30 minutes duration) to average loads as
| well as poor power factor.

The example I am giving is that both customers use the _same_ energy level
(an average of 100 kWH over the month) and both will run a peak kVA and kVAR
at the same high level (and hence the same demand reading). But what the
difference is, when at times other than the peak, one customer has a lower
power factor despite the same energy. So that customer takes more power,
but then gives much of it back each half cycle, netting the same usage and
loss internally as the first customer, but imposing unmeasured (by that meter)
losses on the utility distribution. What I am saying is it can be measured
in terms of measuring both kW(H) and kVAR(H). Each of those figures would
have a rate. The kWH rate would be the usual energy rate. the kVARH rate
would be a secondary energy rate prportioned to the loss that would be
experienced sloshing reactive power around. The first customer would have
a lower kVARH and the second customer would have a higher kVARH, while they
both have the same kWH and kVA peak demand.



| Take another case - steady 100KVA loads - first one at 0.97 pf lag and the
| second at 0.66 pf lag. Each pay $0.08 per KWH so that over the billing
| period (say 720 hours) he will pay $5587 for energy and (at $2/KVA) $2000
| for demand - total $7787 for $0.11 "average cost per KWH"
| The second pays $2000 for the demand charge and $3802 for energy - "average
| cost per KWH" becomes $0.13 per KWH. In this case it would be beneficial for
| the second user to install capacitors.

In this case energy usage is definitely different.


| Another case- first one 100KW steady at 1.0 pf and second 100KW steady at
| 0.66pf lag
| First pays $200+5760=$5960 Second pays $303+7760 =$8063 for the same actual
| energy used.
|
| Third case: both at 100KW average- first as above and the second with a peak
| of 1000kVA- both at unity pf. First pays $5960, second pays $7760
|
| A demand charge based on KVA peaks which exist long enough for equipment to
| reach a steady state operating temperature reflects both the effect of high
| load peaks as well as poor power factor.

Now go with BOTH having a peak of 1000kVA. Both demand meters will read the
same thing (1000kVA peak since reset). It could be a one day long peak. So
they would both have the same demand charge. The rest of the time both use
power such that over the whole month (720 hours) the energy used, including
that used during the one day peak, totals 72000 kWH (the equivalent of 100kW
over 720 hours). So their energy readings will be the same, too. But the
difference is that during the times other than peak, they have different pf.

What I am saying is that kVA demand peak and kWH total energy can still have
exactly the same readings even though the kVAH would differ. The customer
with the lower pf is, of course, putting more load on the distribution due
to more kVAR, but this load isn't contributing to the peak demand since that
one bad day set the peak level. Still, it is overall heating of equipment,
and more importantly, is energy wasted in distribution that does not get
measured by the kWH reading (I'm not talking about what little loss there
is in the customer's own wires, which would be measured by the kWH meter);
I'm talking about the extra current drawn in by the kVAR, not see by the
kWH meter at the customer, but has some partial loss in the distribution
coming in. And that is an energy loss (in addition to anything else).
Maybe we don't need both kW and kVA peak demand readings, but I do think
we need to have both kWH and kVA(R)H readings to measure the cost of the
customer (not just what they benefit from).

We had 'demand metering' at one facility, so we coordinated the starting of
our largest machinery (2000 hp emergency pump started monthly for testing)
and testing our emergency diesel generators (4000 kW EMD's) so the pump
start would *not* be on-grid and affect our monthly demand charge. This is
the type of demand metering that Don seems to be talking about. The motor
start was less than 10 second surge, but it would 'kick the needle' up for
the month.

But you seem to be talking about kVAR metering/charging. I've seen that in
the Detroit area and it *is* a different animal. A couple of industries
that run really poor pf caused a lot of trouble for Detroit Edison. Billing
based on the energy used was not enough. Billing based on 15-minute demand
was not enough. The voltage control DE needed to implement because of the
very poor pf justified VARH metering, in addition to kWH and peak demand.
This was very rare though, I think there was only one or two customers in
the service area that had that. ISTR, in the early 90's, the company got
tired of paying DE and went to some sort of solid-state, electronically
controlled 'condenser' system that could react to the changing var loading
and save them the extra charges. Don't know why they didn't use
'synchronous condensers', *thats* how DE was serving them. Maybe they
didn't have the space for them, but did for electronic version.

daestrom
 
S

SQLit

Jan 1, 1970
0
| We had 'demand metering' at one facility, so we coordinated the starting of
| our largest machinery (2000 hp emergency pump started monthly for testing)
| and testing our emergency diesel generators (4000 kW EMD's) so the pump
| start would *not* be on-grid and affect our monthly demand charge. This is
| the type of demand metering that Don seems to be talking about. The motor
| start was less than 10 second surge, but it would 'kick the needle' up for
| the month.

That is definitely the way to do it to keep down costs.


| But you seem to be talking about kVAR metering/charging. I've seen that in
| the Detroit area and it *is* a different animal. A couple of industries
| that run really poor pf caused a lot of trouble for Detroit Edison. Billing
| based on the energy used was not enough. Billing based on 15-minute demand
| was not enough. The voltage control DE needed to implement because of the
| very poor pf justified VARH metering, in addition to kWH and peak demand.
| This was very rare though, I think there was only one or two customers in
| the service area that had that. ISTR, in the early 90's, the company got
| tired of paying DE and went to some sort of solid-state, electronically
| controlled 'condenser' system that could react to the changing var loading
| and save them the extra charges. Don't know why they didn't use
| 'synchronous condensers', *thats* how DE was serving them. Maybe they
| didn't have the space for them, but did for electronic version.

Yeah, I am talking about that, in addition to other measures. My point is
that a customer can have the same energy usage, and the same demand peak,
and still vary in the reactive power effect on distribution. I think, to
be fair, all factors need to be measured, and charged an appropriate rate
for each. But kVARH (yes, the H is in there) is not a measure of demand,
or how big the equipment to serve the customer has to be, but rather, it
is a measure of how much energy is being LOANED to the customer. It's
rate would be like charging interest on the loan, figured on the basis of
how much real energy is lost in transporting this loaned energy. It is an
energy charge (the wasted energy has to be generated by the energy
provider) and a distribution charge (the wasted energy is a little more
heat load that could add up if other customers are at greater peak demands
at that time). But for most customers, these charges would be small, and
probably do not warrant the cost of measuring them. Still, it is a valid
charge (and should be charged if measuring and billing didn't add to the
cost).

My next argument is that demand metering itself should be measured
differently. Suppose you started that emergency pump on the grid (perhaps
because you didn't have emergency diesel generators). If you do that
during the day, you are putting more load on the grid than if you do that
during the night (generally). You should be charged less for doing that
at night. But of course this would require more sophisticated metering.
Imagine a gang of 96 demand meters, each of which operates only during a
unique designated 15 minute slice of the day. Billing would be done by
multiplying each of the 96 demand levels by the respective rate for that
15 minute slice. Then the monthly demand charge is which of these 96
charges is the highest. Thus if you have a peak demand at night, when the
rates would normally be lowest, and none in the day, your demand charge
would be lower.

Your not the utility. They pick how the rate structures are set due to the
customer that that have. If you were in an area of steel production you
would see higher PF billing rate that just for homes. I know of places on
the eastern seaboard that if a large user fails to keep the PF above 85 they
the utilitiy has the option to disconnect them. My experence of demand
billing is done by using an either fixed or sliding demand window. With an
sub demand window below that of 3 or 5 minutes. They record the maxium
demand in each 24 hours and reset it once a month. This all has to do with
generator capisity. Try northern Mexico or the LA basin for some utility
demand rates that get complicated. Most utilities use Summer and Winter
rates. They also introduce Peak demand, Mid Peak and low. They also use up
to 4 time periods a day. ( at least that is the most I have ever seen).
And I am not mixing up demand and energy. Of course energy rates are
generally lower at night because of greater availability of generating
capacity then. But demand rates would be as well, because you demand
peak, while still stressing the transformers feeding your loads, would not
be stressing the distribution and transmission as much because it is at a
time when the overall demand from all customers is down.

Of course a gang of 96 demand meters is totally impractical. But there is
a way to do this reasonably well with electronic metering. One meter that
measures kWH, kVARH, and peak kVA, separately in each 15 minute period,
and sends the up to 2976 x 3 data points to the billing computer (it would
be no more than about 128K bytes of data), can accomplish all these
measures, and do it all on a time of day, and day of week (do your pump
test on Sunday when many industrial users and commercial office air
conditioners are at reduced load), basis. Computer software can readily
sort out all this data, as well as provide detailed time of day load
trends for engineering to compare with their distribution metrics. This
is what I think the meter of the future (today, really) needs to be. For
the home, a less sophisticated version (cheaper to make because it only
measures kWH in each 15 minute period) would be used.

The problem with a computer data base is that the information becomes huge
very fast. Using the CH PowerNet system I have seen an single meter create
an 40-50 meg file in 30 days. ( 15 minute window and 5 minute sub window) MS
Access crapps out when the data base climbs much over 700 meg. Now what
happens when you miss a time point? You interpolate around it. Bad news if
it was an Peak billing period. The customer billing systems that I have
installed are used for demand side management. They need to know where the
load is going and when. Square D has an system and so does PML. I like the
PML meters because you can install more storage in the meter. CH meters, the
6000/6600 had only a meg of storage when I worked with them. One meg was
only about a weeks worth of data depending on your rate structure.

Here in AZ there are residential demand meters. One used has up to 4 times
of day in it and the other is stricly demand based on a 15 minute window.
The utlilites keep the monthly high for a year. Make a mistake and once and
you are penalized for a year.
When I worked for ASU, the electric bill was around a million a month. Load
varied from 24-28 meg demand in the day time to 30-34 meg demand at night.
Chillers ran only off peak. We were able to choose our demand for a month.
Breaking the bubble as it was called cost $40,000 dollars a meg until the
end of the month. You do not see many night games during the week at Sun
Devil Stadium for this very reason. I called central plant one Monday night
game and told them they had 20 minutes to shed 3 meg. 3 Meg is what the
feild lights draw. They though I was crazy, until the load hit them. I had
worked on the feild light upgrade for the SuperBowl XXX and knew exactly
what the lights drew.
We once measured the feeders to the stadium, just about 130 amps at 15kv.
But when the kick off happen the load dropped to about 90. They were done
cooking and everything was in warmers after kick off. By half time the load
dropped to about 75 amps.

The metering you describe had been available in various forms for more than
10 years maybe longer than that.

http://ka9wgn.ham.org/ |
--------------------------------------------------------------------------
---
 
D

Don Kelly

Jan 1, 1970
0
| |>
|> | That may be true- it was routinely done in the area that I used to live
| in.
|> | Note that KVA demand metering was based on monthly peak where the meter
| had
|> | a thermal(?) lag so that it rode through starting transients and short
| peaks
|> | and represented what was important to the utility - temperature rises in
|> | equipment.
|>
|> Sounds like exactly the right way to measure for the component of costs
|> that relates to purchasing, installing, and maintaining transmission and
|> distribution facilities.
|>
|> So, given 2 customers that periodically have a 1000 kVAR demand, but run
|> regularly around 100 kW, where one of them has pf 0.97 and the other has
|> pf 0.66, how are they going to measure the added charges for the second?
|> A kVAR usage meter?
| ---
| The meters measured kVA (not kVAR) demand and the needle pushed another
| needle so that the peak kVA during the period is registered. Your two
| customers would have the same kVA demand charge as both require the utility
| to provide the same equipment capability but the first would have a higher
| kWH bill as he uses more energy. The effective cost per kWH would be lower
| for him than for the second person. Both are being charged for a high kVA
| (not necessarily kVAR) peak demand because of a fluctuating load and the
| second gets a whammy in this respect from poor pf. The KVA demand
| penalises high peak (over 15 to 30 minutes duration) to average loads as
| well as poor power factor.

The example I am giving is that both customers use the _same_ energy level
(an average of 100 kWH over the month) and both will run a peak kVA and kVAR
at the same high level (and hence the same demand reading).
-------------------
There seems to be some confusion here: 100kWh is, I assume the monthly
energy usage- if so then a peak kVA reading would last for less than 0.1
hours and a demand meter would register a negligable kVA for both loads. If
you are talking about 100kW average for the month (about 720 hours) then the
kWH would be 72000 kWH for both loads. If both loads indeed had a peak of
1000kVA with the pf's that you cited, the first load would have a peak
power of 970kW and the second a peak power of 660 kW but the same kVA peak.
--------------
But what the
difference is, when at times other than the peak, one customer has a lower
power factor despite the same energy. So that customer takes more power,
but then gives much of it back each half cycle, netting the same usage and
loss internally as the first customer, but imposing unmeasured (by that meter)
losses on the utility distribution. What I am saying is it can be measured
in terms of measuring both kW(H) and kVAR(H). Each of those figures would
have a rate. The kWH rate would be the usual energy rate. the kVARH rate
would be a secondary energy rate prportioned to the loss that would be
experienced sloshing reactive power around.

-----------
I have to disagree with you. The energy that is being shuffled around will
not appear on the kWH meter. That is true. The meter (and kW meters) measure
average power. The difference is that 100kW at 0.97 pf will have a kVA of
103 kVA while 100kW at 0.66 pf will have 151.+ kVA. Assuming the same
voltage and line resistances , the internal losses of the second customer
will be (151./103)^2 = 2.16 times that of the first customer. This loss WILL
be registered by the kWH meter and the customer pays for it.
Measuring kVARH will not give any useful information as the customer's
losses are already measured and this information will not be of use in
sizing of equipment or, as a matter of fact, determining the utility losses.
KVA demand will not determine utility losses either but will affect
equipment sizing and costs (a point that you agree with). Utility energy
losses will be determined by utilities measuring the difference between
their generated energy and the customers' usage.
------------

The first customer would have
a lower kVARH and the second customer would have a higher kVARH, while they
both have the same kWH and kVA peak demand.
| Take another case - steady 100KVA loads - first one at 0.97 pf lag and the
| second at 0.66 pf lag. Each pay $0.08 per KWH so that over the billing
| period (say 720 hours) he will pay $5587 for energy and (at $2/KVA) $2000
| for demand - total $7787 for $0.11 "average cost per KWH"
| The second pays $2000 for the demand charge and $3802 for energy - "average
| cost per KWH" becomes $0.13 per KWH. In this case it would be beneficial for
| the second user to install capacitors.

In this case energy usage is definitely different. ---
Right
----


| Another case- first one 100KW steady at 1.0 pf and second 100KW steady at
| 0.66pf lag
| First pays $200+5760=$5960 Second pays $303+7760 =$8063 for the same actual
| energy used.
|
| Third case: both at 100KW average- first as above and the second with a peak
| of 1000kVA- both at unity pf. First pays $5960, second pays $7760
|
| A demand charge based on KVA peaks which exist long enough for equipment to
| reach a steady state operating temperature reflects both the effect of high
| load peaks as well as poor power factor.

Now go with BOTH having a peak of 1000kVA. Both demand meters will read the
same thing (1000kVA peak since reset). It could be a one day long peak. So
they would both have the same demand charge. The rest of the time both use
power such that over the whole month (720 hours) the energy used, including
that used during the one day peak, totals 72000 kWH (the equivalent of 100kW
over 720 hours). So their energy readings will be the same, too. But the
difference is that during the times other than peak, they have different pf.

What I am saying is that kVA demand peak and kWH total energy can still have
exactly the same readings even though the kVAH would differ.
--------
That is true.
---------------
The customer
with the lower pf is, of course, putting more load on the distribution due
to more kVAR, but this load isn't contributing to the peak demand since that
one bad day set the peak level. Still, it is overall heating of equipment,
and more importantly, is energy wasted in distribution that does not get
measured by the kWH reading (I'm not talking about what little loss there
is in the customer's own wires, which would be measured by the kWH meter);
I'm talking about the extra current drawn in by the kVAR, not see by the
kWH meter at the customer, but has some partial loss in the distribution
coming in.
---------
OK, noting that the customer is paying for the additional loss on his side
of the meter due to poor pf.
--------------
And that is an energy loss (in addition to anything else).
Maybe we don't need both kW and kVA peak demand readings, but I do think
we need to have both kWH and kVA(R)H readings to measure the cost of the
customer (not just what they benefit from).
-------
The problem is that with both kVA(R)H and kWh readings you still do not have
a handle on the utility's losses. Only if the loads were constant over the
metering period would you get such information and even then it would be
only after some "D'Bougerre" factoring.

Consider a load at 1.0 pf which is at 10kW for 9 hours and 100kW for 1 hour.
in the 10 hour period the energy usage would be 190kWH and kVAH would be
190kVAH (kVARh =0). Note that the current would be (at 1000V) 10A for 9
hours and 100A for the remaining hour. For a fixed resistance of 0.1 ohms
equivalent the loss would be 10 watts for 9 hours and 1000 watts for the
remaining hour. The watthour meter will show 190 +0.09 +1.0 =191.09 kWH and
the customer would be billed accordingly.

At a load of 19 kW for 10 hours the kWH reading would be 190.1 kWH
including losses. The kVAH and kVARH values will be the same in both cases.
The kVA peak would only be 19+kVA.

Now consider a load which is 190kW for 1 hour-and 0 for 9 hours. same kVAH
and kVARH but the metered power is now 190+(190)^2*0.1=193.6 kWH The kVA
peak would be 194- kVA.

In all cases the customer is paying for his own losses. This is true at
any power factor. The increase in utility losses is NOT reflected in kVAH
or kVARH readings which integrate losses. kVA demand in the 3 cases is 100,
19 and 190 respectively. with losses of 1.1, 0.1 and 3.6 kWH respectively.
The same sort of situation would occur at any pf. The customer's energy
charge picks up the customer's loss but neither kVAH or kVARH readings have
any relationship to the utility or customer energy losses that are incurred
and serve no purpose. In fact kVA demand, in this set of examples, is a
better measure- but it is, admittedly, not a good measure. It is a good
measure for equipment costs and sizing (and kVA(R)H is not useful in this
respect).
In fact, the utility measures its generation and the loads and from these
gets a handle on the losses which then is a factor in the rates that are
set. (i.e. generate 100,000,000MWH at $30/MWH and sell 90,000,000 MWH
Cost of power delivered is 10/9*$30=$33.3/MWH + operating cost, interest
and depreciation, taxes, and return to the investor and the customer cost
will be well above $33.3/MWH or 3.3 cents/KWH- say 10cents/kWH?

Please do not trust my math- it is affected by vino. In addition, I think
that we are headed in the same direction, eventually. Much easier one on one
over a beer. :)

--
Don Kelly
[email protected]
remove the urine to answerhttp://ka9wgn.ham.org/ |
--------------------------------------------------------------------------
---
 
D

Don Kelly

Jan 1, 1970
0
daestrom said:
beneficial steady a equipment

We had 'demand metering' at one facility, so we coordinated the starting of
our largest machinery (2000 hp emergency pump started monthly for testing)
and testing our emergency diesel generators (4000 kW EMD's) so the pump
start would *not* be on-grid and affect our monthly demand charge. This is
the type of demand metering that Don seems to be talking about. The motor
start was less than 10 second surge, but it would 'kick the needle' up for
the month.


-------------
Interesting- the demand meters that I have seen (and tested one about 50
years ago) had a thermal lag such that the reading would take about 20 to 30
minutes to reach 90% of the actual kVA in a steady situation. In 10 seconds
the "kick" would be very small if any. The recognition that motor starting
occurs and does not normally have any real effect on equipment heating was
recognised. Repeated starts- another animal but I bet there were limits on
how often the pump could be started.

As for the VARH metering - in fact this appears to be a case of a specific
solution to a specific situation. Again, interesting- thanks.
 
D

Don Kelly

Jan 1, 1970
0
| We had 'demand metering' at one facility, so we coordinated the starting of
| our largest machinery (2000 hp emergency pump started monthly for testing)
| and testing our emergency diesel generators (4000 kW EMD's) so the pump
| start would *not* be on-grid and affect our monthly demand charge. This is
| the type of demand metering that Don seems to be talking about. The motor
| start was less than 10 second surge, but it would 'kick the needle' up for
| the month.

That is definitely the way to do it to keep down costs.


| But you seem to be talking about kVAR metering/charging. I've seen that in
| the Detroit area and it *is* a different animal. A couple of industries
| that run really poor pf caused a lot of trouble for Detroit Edison. Billing
| based on the energy used was not enough. Billing based on 15-minute demand
| was not enough. The voltage control DE needed to implement because of the
| very poor pf justified VARH metering, in addition to kWH and peak demand.
| This was very rare though, I think there was only one or two customers in
| the service area that had that. ISTR, in the early 90's, the company got
| tired of paying DE and went to some sort of solid-state, electronically
| controlled 'condenser' system that could react to the changing var loading
| and save them the extra charges. Don't know why they didn't use
| 'synchronous condensers', *thats* how DE was serving them. Maybe they
| didn't have the space for them, but did for electronic version.

Yeah, I am talking about that, in addition to other measures. My point is
that a customer can have the same energy usage, and the same demand peak,
and still vary in the reactive power effect on distribution. I think, to
be fair, all factors need to be measured, and charged an appropriate rate
for each. But kVARH (yes, the H is in there) is not a measure of demand,
or how big the equipment to serve the customer has to be, but rather, it
is a measure of how much energy is being LOANED to the customer.
rate would be like charging interest on the loan, figured on the basis of
how much real energy is lost in transporting this loaned energy. It is an
energy charge (the wasted energy has to be generated by the energy
provider) and a distribution charge (the wasted energy is a little more
heat load that could add up if other customers are at greater peak demands
at that time). But for most customers, these charges would be small, and
probably do not warrant the cost of measuring them. Still, it is a valid
charge (and should be charged if measuring and billing didn't add to the
cost).

-------------
The problem is that the customer returns this energy within the period (1/60
second) that it he used itIt is not an "energy charge"- loaned or
otherwise. What interest would be charged on a loan for 1/2 of a cycle? It
is being charged through the energy metering. In addition, as I have said
earlier this evening- KVARH metering does not reflect the actual losses seen
by the utility.
In the case above it is not an energy related issue but a voltage control
issue which so far is quite a specific situation.
--------------
My next argument is that demand metering itself should be measured
differently. Suppose you started that emergency pump on the grid (perhaps
because you didn't have emergency diesel generators). If you do that
during the day, you are putting more load on the grid than if you do that
during the night (generally). You should be charged less for doing that
at night. But of course this would require more sophisticated metering.
Imagine a gang of 96 demand meters, each of which operates only during a
unique designated 15 minute slice of the day. Billing would be done by
multiplying each of the 96 demand levels by the respective rate for that
15 minute slice. Then the monthly demand charge is which of these 96
charges is the highest. Thus if you have a peak demand at night, when the
rates would normally be lowest, and none in the day, your demand charge
would be lower.
----------
My initial comment was "Does the size and cost of a utility transformer and
lines feeding a specific plant depend on the time of day? If it were so,
then your suggestion would be great." However, I think that you are going
beyond this - doing "time of day" to bias the demand rate as is now done in
many cases for energy rates. Interesting but considering that the demand
charges are mainly related to the cost of equipment to supply a particular
load ( further back in the system the effect becomes more diffuse so the
costs of the immediate feed to the customer is the only one that can fairly
be attributed to that particular customer- the more diffuse costs are built
into the energy rate) and the equipment isn't going to change on a 15 minute
cycle- there is a problem. What sort of "demand" metering most accurately
represents costs?

You are absolutely right in suggesting that such testing be done at night or
off-peak times- The KVA demand is reduced and if time of day metering of
energy is in place, the energy cost would also be reduced.
Note that many large industries negotiate energy contracts which have a kVA
limit- if the peak kVA is below a certain value then a "good" energy rate is
available:-BUT if the kva demand exceeds this limit- the energy charge
increases drastically. Many industries with their own generation, use such
generation to shave the peaks and keep the charges from the utility down. If
one has such capability it works well to the advantqage of both the utility
and the customer. Many moe utilities use some form of pf correction-
reduction of kVA demand as well as improved voltages.
--------------
The advantage would be there.
And I am not mixing up demand and energy. Of course energy rates are
generally lower at night because of greater availability of generating
capacity then. But demand rates would be as well, because you demand
peak, while still stressing the transformers feeding your loads, would not
be stressing the distribution and transmission as much because it is at a
time when the overall demand from all customers is down.
--------
The idea is great but the problem is that back in the system- your load is
absorbed into a melting pot. What demand that is measured at a customer
level can be isolated as chargeable to that customer. How much effect that
it has further up the chain depends on the size of that customer with
respect to the sum total of all customers. Load diversity rears its head as
well. Demand charges are meant to address costs associated with supply to a
specific customer rather than overall system costs. .
Can this be extended to consider overall system costs - in theory - Yes.
However, in practice, when the cost of getting the data exceeds the saving
gained from use of the data- don't bother.
--
Cheers,
Don Kelly
[email protected]
remove the urine to answer
Of course a gang of 96 demand meters is totally impractical. But there is
a way to do this reasonably well with electronic metering. One meter that
measures kWH, kVARH, and peak kVA, separately in each 15 minute period,
and sends the up to 2976 x 3 data points to the billing computer (it would
be no more than about 128K bytes of data), can accomplish all these
measures, and do it all on a time of day, and day of week (do your pump
test on Sunday when many industrial users and commercial office air
conditioners are at reduced load), basis. Computer software can readily
sort out all this data, as well as provide detailed time of day load
trends for engineering to compare with their distribution metrics. This
is what I think the meter of the future (today, really) needs to be. For
the home, a less sophisticated version (cheaper to make because it only
measures kWH in each 15 minute period) would be used.
http://ka9wgn.ham.org/ |
--------------------------------------------------------------------------
---
 
D

daestrom

Jan 1, 1970
0
Don Kelly said:
-------------
Interesting- the demand meters that I have seen (and tested one about 50
years ago) had a thermal lag such that the reading would take about 20 to 30
minutes to reach 90% of the actual kVA in a steady situation. In 10 seconds
the "kick" would be very small if any. The recognition that motor starting
occurs and does not normally have any real effect on equipment heating was
recognised. Repeated starts- another animal but I bet there were limits on
how often the pump could be started.

Well, *most* of our motors and loads were under 500 hp. But the two
emergency pumps were so much larger than any others that it warranted the
effort to coordinate with DG testing. Your thermal-equivalent makes sense
to me too, but what we had was a near instantaneous 'peak demand' recorder.
Highest peak during the month cost us an extra fee. Not sure if it was just
thermal KVA rating of utility equipment, or a 'penalty' for the voltage dip
we caused on the utility lines. But it was there, so we dealt with it.
As for the VARH metering - in fact this appears to be a case of a specific
solution to a specific situation.

Yeah, very specific case. As I said, only saw this on one or two customers.

daestrom
 
D

daestrom

Jan 1, 1970
0
SQLit said:
starting This that

Your not the utility. They pick how the rate structures are set due to the
customer that that have. If you were in an area of steel production you
would see higher PF billing rate that just for homes. I know of places on
the eastern seaboard that if a large user fails to keep the PF above 85 they
the utilitiy has the option to disconnect them. My experence of demand
billing is done by using an either fixed or sliding demand window. With an
sub demand window below that of 3 or 5 minutes. They record the maxium
demand in each 24 hours and reset it once a month. This all has to do with
generator capisity. Try northern Mexico or the LA basin for some utility
demand rates that get complicated. Most utilities use Summer and Winter
rates. They also introduce Peak demand, Mid Peak and low. They also use up
to 4 time periods a day. ( at least that is the most I have ever seen).


The problem with a computer data base is that the information becomes huge
very fast. Using the CH PowerNet system I have seen an single meter create
an 40-50 meg file in 30 days. ( 15 minute window and 5 minute sub window) MS
Access crapps out when the data base climbs much over 700 meg. Now what
happens when you miss a time point? You interpolate around it. Bad news if
it was an Peak billing period. The customer billing systems that I have
installed are used for demand side management. They need to know where the
load is going and when. Square D has an system and so does PML. I like the
PML meters because you can install more storage in the meter. CH meters, the
6000/6600 had only a meg of storage when I worked with them. One meg was
only about a weeks worth of data depending on your rate structure.

I can attest to that. While working with DTE during 'deregulation', they
had to supply a new meter to any industrial customer that wanted to buy
power from an independent. These meters required that the customer have a
dedicated phone line next to the meter. The meters were setup to 'phone
home' once a week and download their 15-minute readings to DTE. If the line
was busy or what-have-you, the meter would keep trying and store the
information for as long as it could. How to deal with 'missing' data was a
tangled issue with the service commission.

Then all the meter readings had to be allotted to each IPP and compared with
their scheduled power. If the IPP generated more or less than their
customers used, $$$ for DTE. Reconciling the monthly scedules of IPP's
along with non-metered, and DTE customers was a b----.

daestrom
P.S. You should have seen the number of ad-nauseum meetings about even such
straightforward things as setting the clocks ahead/back each year for
Daylight Savings Time ;-)
 