What is line current ?

M

mowhoong

Jan 1, 1970
0
I have a 10 hp power water pump which on 420 volts 3 phase, my
calcalation would be 12.8 A
line current, which mean each phase draw 12.8 A is that correct ?
Can any person help me in this question. Thanks
Regards
 
P

Paul E. Schoen

Jan 1, 1970
0
mowhoong said:
I have a 10 hp power water pump which on 420 volts 3 phase, my
calcalation would be 12.8 A
line current, which mean each phase draw 12.8 A is that correct ?
Can any person help me in this question. Thanks
Regards

420 volts phase to phase is about 242 volts to neutral. 10 HP is 7460
watts, so total current is 30.76 amps, or 10.25 amps per phase. But there
could be power factor and efficiency issues that would cause the current
draw to be 12.8 amps with output power of 10 HP.

Paul
 
M

mowhoong

Jan 1, 1970
0
420 volts phase to phase is about 242 volts to neutral. 10 HP is 7460
watts, so total current is 30.76 amps, or 10.25 amps per phase. But there
could be power factor and efficiency issues that would cause the current
draw to be 12.8 amps with output power of 10 HP.

Paul

Hi Paul. Thanks for your reponse. My water pump connection on 3 phase
do not have neutral, if I include the 0.8 on power
factor and efficiency it will have 16 A line current right ?
Regards
 
P

Phil Allison

Jan 1, 1970
0
"mowhoong"

Hi Paul. Thanks for your reponse. My water pump connection on 3 phase
do not have neutral, if I include the 0.8 on power
factor and efficiency it will have 16 A line current right ?


** Post your math - wanker.

Cos we all need a good laugh.



......... Phil
 
G

gearhead

Jan 1, 1970
0
"mowhoong"

Hi Paul. Thanks for your reponse. My water pump connection on 3 phase
do not have neutral, if  I include the 0.8 on power
factor and efficiency it will have 16 A line current right ?

** Post your math  -  wanker.

  Cos we all need a good laugh.

........  Phil

I'm laughing right now. You bring sunshine to my day.
 
B

bud--

Jan 1, 1970
0
mowhoong said:
I have a 10 hp power water pump which on 420 volts 3 phase, my
calcalation would be 12.8 A
line current, which mean each phase draw 12.8 A is that correct ?
Can any person help me in this question. Thanks
Regards

The US National Electrical Code gives 14A, 460V as typical for a 10HP
motor. Converting that would be 15.3A at 420V as typical.

Actual values depend on power factor and efficiency as mowhoong posted.
They also depend on whether the pump is developing 10HP. The power
depends on the head pressure.

No information plate on the pump?
 
I have a 10 hp power water pump which on 420 volts 3 phase, my
calcalation would be 12.8 A
line current, which mean each phase draw 12.8 A is that correct ?
Can any person help me in this question. Thanks
Regards

Yes, your answer is correct. Each phase draw 12.8A
 
P

Paul E. Schoen

Jan 1, 1970
0
420 volts phase to phase is about 242 volts to neutral. 10 HP is 7460
watts, so total current is 30.76 amps, or 10.25 amps per phase. But there
could be power factor and efficiency issues that would cause the current
draw to be 12.8 amps with output power of 10 HP.

Paul

Hi Paul. Thanks for your reponse. My water pump connection on 3 phase
do not have neutral, if I include the 0.8 on power
factor and efficiency it will have 16 A line current right ?
Regards

The effective phase-to-neutral voltage (which is the vector component in
phase with current at zero PF), is V(phase-phase) / sqrt(3). 10 HP = 7460
watts / 242 V = 30.8 A /3 = 10.2 A per phase. You should never see 16 amps
line current except on start-up. But a 0.8 factor on the 10.2 A gives 12.8
amps.

Paul
 