240 volts vs. 208 volts in a residential building
Which of the following methods of wiring a large residential building
would be preferred between these two choices (there certainly are other
choices, but I'm focusing on these two right now).
The building is supplied by power at 480Y/277 volts, or at a higher
voltage stepped down in a secured electrical room to 480Y/277. One or
more large capacity 480Y/277 volts circuits feed through the vertical
core of the building to an electrical room on each floor. On each
floor, a dry-type transformer steps 480 volts down to service voltage
for each customer.
1.
Each floor is powered through a three phase transformer that steps the
480Y/277 volt subfeed down to 208Y/120 volts. Each tenant is supplied
with just TWO phases of the three phase service, with the choice of
phases approximately balanced.
2.
Each floor is powered through a single phase transformer that steps
just two legs of the 480Y/277 volt subfeed from 480 volts to 240/120
volts. Each tenant is supplied with this normal single split phase
voltage. The diversity of the floors are approximately balanced.
For both of these cases, assume the total load is within the capacity
of available transformers, or that multiple transformers could be used
to supply each floor when there is a greater load than one transformer
can supply. Also assume that special building-wide loads such as
elevators and centralized HVAC can be powered by 480Y/277 directly if
applicable, or by a voltage system derived from 480Y/277 as needed.
As a variation of choice #2, where more than one transformer is needed
for a building with large floors, these transformers can be balanced
as reasonably possible over the core subfeed phases. Also assume that
additional subfeed circuits can be separately wired if a single feed
would be inadequate, up to as many feeds as needed, such as one feed
separately to each floor.
I'm not specifying a particular size for this building. Instead, what
I want to focus on is the practicality of supplying 120/240 volts for
single phase tenants (and generally residential will be single phase)
instead of 120/208 volts.
Another question: would this preference be any different if some or
all of the tenants were light business use, such as lawyer offices,
corporate branch sales offices, recruiters, etc, with no unusual
electrical needs (but would have a small kitchen with normal cooking
facilities for employee use such as lunch breaks)?
208 sucks in a residential building unless the landlord owns the
laundry, provides HVAC and all the heat producing appliances are
fossil fuel.
Consumer grade dryers, ranges, water heaters and A/C units are
designed for 240. You can 208 volt equipment but it costs more and
the output of 240v heaters at 208 is significantly less.
John Gilmer
Personally, I would prefer single phase 120/240 over a "2 out of 3" 120/208
service.
There is, maybe, a better selection of 240 volt over 208 "stuff" including
office equipment.
OTOH if someone "needed" 120/208 3 phase with the help of a two transformers
he could "reconstitute" is from the 3 wire 120/208.
I
Beachcomber
fossil fuel.
I agree that 208 sucks and is to be avoided if possible, but you can
purchase electric range heater elements and dryer conversion kits for
208V. It's a pain in the A though if residents don't understand and
buy or bring the wrong replacement equipment. A 240V dryer running on
208V, in my experience will run a lot longer to dry the clothes
properly.
Of course if you have gas ranges and gas dryers, it doesn't matter.
The larger (portable) air conditioners are rated for 240V and you may
have trouble finding one that works OK on 208v. Fixed AC (compressor
units are usually rated for 240v but sometimes wired on 208V.
circuits. Then there might be elevator motors, sump pumps, air
handlers, vent fans and other motors to consider.
Beachcomber
| fossil fuel.
Exactly.
There are 208 volt elements for many things, but not all. That itself
is clear indication that 208 volts for 240 volt stuff sucks.
|>fossil fuel.
| properly.
Not all ranges have 208 volt elements available. Some do. Most don't
as far as I've seen. The more expensive ones seems to be the ones that
do, but you're just tossing out a fine 240 volt element after special
ordering a 208 volt element.
I have seen some for 208 volts. But not very many. And those were
commercial units for motels.
IMHO, three phase should be limited to 480 volts in the USA.
| service.
| office equipment.
You probably mean:
A *
N C
But it still doesn't solve the 240 volt problem.
Ben Miller
for each customer.
1.
Nothing unique about this. It is common. In fact, I saw one today. The
distribution panels in the metering room on each floor are three-phase, each
tenant gets 208/120 single phase. I don't know what 240 volt loads are in
the units. If you use gas for the cooking and laundry, the entire issue of
208 vs. 240 in the tenant units goes away. The only other load would be A/C,
and those are normally dual rated for 230/208 volt.
2.
Distributing three phase is more efficient in terms of the wiring, panel,
and transformer cost. At the same voltage, you can carry 73% more power with
33% more copper (25% more copper if you have an egc as well).
Often done. Not a problem.
Talk to some building owners about what they are willing to pay for extra
transformers and wiring just so their tenants can have 240/120 volts instead
of 208/120, and I think you will see the practical problem. I have clients
(owners) trying to squeeze every last penny out of the cost of the
electrical systems in these buildings. They just aren't going to buy into
the extra $$, when there really isn't any problem. If appliances were
failing every week, that would be different.
Nope. Many of those buildings also use 208/120 four wire. It is all about
the cost of distributing the power through the building. There is no
compelling reason to add cost or complexity.
Ben Miller
John Gilmer
| service.
| office equipment.
You probably mean:
A *
N C
Quite correct. I just wanted to give the ONLY reason to give the units
120/208 over 120/240.
I'm definitely on the 120/240 side.
Old Tom Edison got it right the first time!
BTW: That is a VERY good ASCII representation of the way of generatig the
3rd phase.
| |> On Wed, 29 Nov 2006 21:16:45 -0500 John Gilmer <[email protected]>
| 120/208
|> | service.
| including
|> | office equipment.
| transformers
|> You probably mean:
|> A *
|> N C
|> B
| 3rd phase.
Well, Tom had part of it right. I'm still fence sitting on the DC thing.
AC is certainly more practical right now because everything is designed
around it ... just as so many things are designed around 240 volts instead
of 208 volts.
I wonder what the power company would think if I put big single phase loads
on that derived C-N connection :)
|> for each customer.
|> 1.
It is in fact A/C that I had my first real life experience with that
taught me why 208 is bad when things are designed for 240. After
several burnouts of the A/C blower motor, the service people finally
had to special order a 208 volt motor. The motor will run on a lower
than normal voltage, but during peak heat, our computer room drove it
to nearly continuous operation. The ambient heat plus extra current
heat apparently rose it above the heat some part of the motor just
could not withstand for the time periods involved.
I don't see where you get those exact figures. I know three phase can
be more efficient to distribute power, but those numbers don't seem
right. By saying "33% more copper" that sounds like you are going from
a 3-wire Edison style single phase to a 4-wire Wye derived three phase
with the same size conductors. But that doesn't give 73% more power.
Assuming the same L-N voltage, it's only 50% more. Assuming the same
L-L voltage, it's only 57% more. And if you dismiss the neutral in
both cases, which forces assuming the same L-L voltage, then you are
increasing the copper by 50% to go to three phase, with the 57% power
increase, for a net gain of 15.47% efficiency for the same amount of
copper.
One can always increase the efficiency of "copper" by increasing the
voltage. The conducting material doesn't really care. The insulating
material sure does. Of course you have to weigh the comparitive costs
and I do believe copper is pretty damned expensive. So is aluminum
(which utility transmission and distribution tends to use).
In most cases, appliances won't fail; they will just underperform. For
example an electric water heater takes longer to recover on 208 volts
than if on 240 volts. Penny pinching owners won't want to pay extra to
get water heaters with special 208 volt elements.
This is also wasteful on energy costs. Heating elements are generally
thermostatically controlled (watch the red glow going on and off with
a glass-top range). At 208 volts (compared to 240 volts) they will be
drawing 86.6% of the current but only providing 75% of the heat. This
means they will be switched on 33% more (133% total) time. That means
there is a 15.47% extra energy loss in the wiring.
So really, the penny pinching owners are shifting the costs to the
tenants, even if both parties don't even realize it.
So home much more does a 75 kVA single phase transformer cost over that
of a 75 kVA three phase transformer? My first scenario is to run each
floor on just one of the phases, not be split up three ways. If 75 kVA
is enough for the floor (4 apartments, as an example), this would work.
More likely, they would end up not running 480 volt feeds to transformers
on each floor, especially if the building is small (say 3 to 6 floors).
They'd put in a big 208Y/120 transformer coming into the building, maybe
as a pad mount out back, and just run everything from that.
They could run full three phase to each apartment and put in a three
phase panel. Then just hook appliances within at various phases and
put each apartment in different rotation offsets to diversify things
well. But they don't. It's actually _more_ expensive to do that, at
least for the cost of a branch breaker panel (home comsumer demand and
competititon has certainly driven down the price of single phase panels
in the 100 to 200 amp range).
| Ben Miller
When I was around age 7 or 8 or so, I remember that my grandfather had a
brownout problem. The power company was unable to deliver full voltage
for a day or so. The voltage was something like 15% or 20% less. While
lights did work, the electric stove just didn't even work at all. His
freezer compressor (ran on what was supposed to be 120 volts) burned up.
One big issue in this scenario was that he actually had three phase power
at presumably 208Y/120 volts. He got that because he powered his wood
shop in the back of the house with it since several of his big machines
specifically used three phase (and presumably were designed for 208 volts).
The problem with the stove, though, was that it was dealt a double blow
in brownout effects. It was a normal home model presumably intended for
240 volts. It was being run on 208 volts. With the brownout at say 15%
it was now getting only 177 volts.
The point here is this. Things designed for 240 volts might well work
fine over the whole range of voltage they could get when connected at
240 volts, and work fine when getting the true nominal voltage when
connected at 208 volts. But run them at the lower end of the voltage
range when also connected at 208 volts, and this is pushing things to
the extreme. If the 240 volt appliance can in fact operate OK all the
way from 200 volts to 280 volts actual, putting it on what is nominally
at eaither far end could be a problem when that supply voltage swings
away from that nominal voltage the more extreme way.
If the appliance can operate at + or - 20% around its designed nominal
voltage, and the utility supply can vary by + or - 10% long term and
an additional + or - 10% short term, AND if you intentionally connect
the appliance to only 86.6% of the voltage, then it really can end up
being out of range at least sometimes ... when that 86.6% voltage ends
up actually being really just 73% of the voltage.
How much of a range would an appliance need to support to be able to
handle the FULL high swing from a 240 volt connection to the FULL LOW
swing of a 208 volt connection.
Matthew Beasley
I lived in two apartment complexes prior to buying my first home. Both were
larger complexes and both had 120/240 distribution. The utility provided
multiple services from single phase pad mount transformers. I'm assuming
that given the size of the complex, the primary was three phase with the
transformers distributed among the phases.
Matthew Beasley
were larger complexes and both had 120/240 distribution. The utility
provided multiple services from single phase pad mount transformers. I'm
assuming that given the size of the complex, the primary was three phase
with the transformers distributed among the phases.
I guess I didn't finish my point, so here goes:
A distribution transformer has about the same cost and efficiency going from
primary voltage to either 480V or 240V. If you add the extra intermediate
voltage of 480V, there is the extra cost of transformers and the extra loss
of transformers to go from 480V to 240V. This is offset by the lower losses
and lower cost in SOME of the distribution equipment, mostly the wires.
480V panels tend to be more expensive than 240V for the same power at the
lower power end of things - like an apartment would be. In an industrial /
commercial application, much of the load is at 480V. The lighting,
elevators and HVAC can all be run at 277Y/480V. Only a small fraction of
the load ends up being double transformed. I have seen buildings designed
with both 480V and 208V service from the utility. I expect that the loss
with this type of service would be the lowest. In an apartment complex,
only a small amount of the load could be utilized at 277Y/480V. Most would
be double transformed, so the extra transformer loss would be more
significant.
The point I made above is that a complex could be feed by a multiple of
three single phase services. That would give 120/240 to everyone. That
would give the utility reasonably balanced load.
One more thing to consider is the dislike many utilities have for delta
connected transformers. I talked to a utility engineer since our least
thread on this subject about the common 480V to 120Y/208V in commercial and
industrial buildings. He indicated that he would actually prefer that they
were wired Y-Y, but realizes that won't happen. He said that they don't
amount to too much of a problem because they are such a small fraction of
the load - usually 25% or less. In a shorted phase or ferroresonance
incident, the primary breaker of the transformer often trips because it's so
much smaller than the large transformer feeding the service. The other
common line to line loads are motors. In a phase loss or power loss
situation, they usually trip off line so they are not a problem. Motors
also don't cause ferroresonance like a transformer does.
Matthew Beasley
instead of 208/120, and I think you will see the practical problem. I have
clients (owners) trying to squeeze every last penny out of the cost of the
I major gripe I have with many of the apartment complex developers is the
choice of resistance heat. The owner pays for the equipment, but the tenant
pays the power bill. That usually leads to the cheapest equipment and
maintenance cost but highest operating cost choice of electric heat. I'm a
fairly hands off the market person, but I'm almost willing to support
legislation on more efficient heat for apartments.
Don't forget to also include a requirement for an abundance of high R factor
insulation in the exterior walls, and even between apartments (FYI, I set my
thermostat to 15C in winter, which is well below what most people set it at,
so I'm effectively taking heat from neighbors that are usually at 20C).
Those willing to be less intrusive on how to construct the buildings could
instead simply mandate disclosure of things like the total insulation value
or the heat loss rate for the unit. But most consumers won't understand
these figures.
How many of you "smart" engineers know how much your credit card companies
are ripping you off for? Businesses make money off of consumer ignorance
and actively fight legislation to inform consumers, even when most of them
wouldn't even understand the information.
I'm all for mandating savings ... except I'll keep (and pay for) incandescent
lights in my kitchen. As long as I'm the one paying for the energy, I should
have that right. If I build an apartment building, I would be expected to
put energy saving lights in, however.
That's not really hard to do. The last apartment I lived in was 120/240
(little single phase pads for each building). The one before that (the
one with the master metering mentioned in another newsgroup) was a big
tall three phase cabinet pad mount with a rather deep reservoir section,
serving a cluster of several buildings (about 18 buildings of 16 units
each). Good money says it was 120/208, but I never checked. The range
and A/C at least worked, and the hot water was centrally supplied.
I never had occaision to see what kind of fault current it provided.
But say you are building a 16 floor apartment building with 8 units per
each of the 15 floors above the ground floor. Would you want to power
that whole thing from a single 208Y/120 transformer and potentially have
to pay for all the extra interruption series ratings because such a beast
might put you too close to, or over, the typical 22 kVA interrupt level?
My inclination would be 480 up the core and rotating the taps on it and
put a single phase 480 to 120/240 dry transformer on each floor. Three
phase loads, like elevators, could run on the 480. Exterior HID lights
could run on 277. The lobby floor might well end up with 208Y/120 from
it's own dry transformer to service a small restaurant or two (which
generally does have 208 volt rated equipment available).
If someone does want to do the load calcs on a building like that for fun,
pick some apartment size for each and have a go at typical values and see
what you really come up with given the diversity. Of course it would all
be in fun since there are no real specifics on a hypothetical building.
How big of a building would you say it would have to be to make even 480
not enough voltage for the core feed?
| significant.
It's going to be double transformed whether the tenants get 120/240 or
120/208 or 208Y/120, unless the main transformer outputs 208Y/120.
If it's a tall building, that could be done with the 2nd transformer on
each floor or groups of 2 or 3 floors, depending on practical sizing.
So how about running 832Y/480 up the core and make the utility happy, and
you can still use the common 480 to 120/240 single phase transformers. If
it means more reliable service to the tenants, and doesn't cost much more,
I wouldn't care. But the big issue is getting the entrance transformer,
wiring, and panels to support 832Y/480. For smaller buildings, 416Y/240
might be an option where the single phase transormers are wired for a 240
volt primary. The problem is the upper end of LV tends to be 600 volts
L-L, and some cheaper stuff is only 480 L-L and 277 L-N. So maybe 416Y/240
is about their only option (and now you have to special order elevators and
HVAC for the unusual 416Y/240 or double transform that, too).
Still thinking about this ... if a building is fed by a MV -> 480Y/277 that
is Y-Y as the utility likes for it to be, how much of a problem would exist
if all the transformers fed by this 480Y/277 were single phase connected
L-L at 480 volts in and 120/240 out? That's not a delta. If one phase is
lost coming in to the main Y-Y transformer, that's simply going to be one
phase dead on the 480Y/277 side, and 2/3 of the building w/o power. But
what other problems could exist with that? What problems could happen if
there was a major short on the secondary side of one of the single phase
transformers (aside from hopefully tripping only the minimum breaker that
is necessary)? Would there be any reason for excessive breaker trips if
they are all coordinated correctly? Would making all the sub-transformers
single phase effectively solve the delta connected transformer problems as
the utility sees it?
John Gilmer
They would prefer it over drawing 240 volts on one phase only.
That's the "other reason" the 120/208 is popular: large loads at least draw
from 2 phases. Seems like "around here" the power company just doesn't
like "weird" 3 phase arrangements anymore. New service is Y or single
phase. It may have something to do with deregulation: the local
distribution company might have to pay a penalty for "unbalanced" draws from
suppliers. Before de-reg it was all in the same company.
| loads
If the one load is given a voltage in the C-N phase angle, but the only
connections are A and B, how does this affect the current phase angles?