240 volts vs. 208 volts in a residential building
John Gilmer
If the one load is given a voltage in the C-N phase angle, but the only
connections are A and B, how does this affect the current phase angles?
Off hand, they would be 60 degrees off from the AB and 30 off from AN.
I guess the "next question" is WTF happens with reactive or harmonic loads.
I don't know. Also, I'm too lazy to figure it out right now but maybe the
urge will increase during the day.
In this case we have:
A * A
N C pretending to be N---C (120 per leg)
B B
It would seem to me that N-C or C-N is 90 degrees off from A-B. N-C would
be 120 degrees off from A-N or B-N (each in an opposite way). The power
factor seen in the current on A or B with respect to A-N and B-N voltage
would by my thinking be 0.5. So for 100 amps on N-C there would be 100
amps on N, and also 100 amps on each of A and B.
Someone else was suggesting that if a load has a current which is N degrees
offset from its voltage (e.g. reactive if N!=0), and that voltage came from
2 or more windings with mixed phasor angles (e.g. either of the case of how
to derive 3 phases from 2 120 degree phases, or the angled buck-boost case
I described elsewhere with a B/B winding that was 30 degrees offset from the
winding it was bosting) that the current would somehow change as it goes
through the core to the primary winding such that the N degrees relationship
between voltage and current would be preserved in the primary as seen by the
source supply. That didn't see right to me, but I wasn't absolutely sure if
there was something else going on.
John Gilmer
OK. In the case of the "derrived" C, in general (even with a 100%
resistive load) the current through the transformers will not be in phase
with the voltage across the windings. So, the AB currents will be 60
degrees out of phase of the AN or BN voltage.
source supply.
Nope!
Transformers do a very good job by making the primary current equal to the
secondary current (with the allowance for the current needed to magnetize
the core and, of course, the turns ratio.)
There may be "something" else going on upstream. For example, a
transformer powering the 120/208 3 wire arrangement would "see" a power
factor less than 1.0.
This kind of stuff is tedious. Since I don't get paid to look at such
things I don't worry much about what an unbalanced load "looks" like at the
end of, say, 200 miles of transmission line. I hope it's not too nasty but
I just don't know. Maybe one of the "Power Pros" on this list will
enlighten us.
(Slight OT: some time ago one of the "power pros" tried to enlighten me on
why you can't transmit AC power more than a certain distance. The lesson
didn't completely sink in but maybe I will try again as a mental exercise.)
Matthew Beasley
But say you are building a 16 floor apartment building with 8 units per
each of the 15 floors above the ground floor.
We obviously were thinking of different type of apartments. I was
considering the suburbia type with lots of area on three floors. You're
considering the more urban tower type. This would be completely out of the
range of anything I have experience with.
I've lived in a complex which had a little single phase pad for each
building, and in a different complex which had a big three phase pad
for several buildings together. I have no idea what the design reasons
were. I suspect the former had 120/240 and the latter had 120/208 in
each apartment. I am trying to get a grasp on the why of decisions like
these. One thing I want to know is the power company influence on it.
Ben Miller
Typically these are decisions made by the electrical engineer. As you have
observed, there are several approaches to powering a campus. The large
transformer could also be 480 volt or higher, with individual transformers
in each building. There could be non-electrical factors also, such as
available space for transformers, new construction vs. remodeling, etc.
In my experience, the utility will do whatever you ask for, within the
limits of what they have available. They do review your load application,
but I have never had them reject one. They might charge you to bring a
particular voltage to the area if it isn't within a certain distance
already, but they will generally do it. For large industrial facilities,
they get more involved because of the loading on their system.
Ben Miller
So if I were to build a large apartment building, even though the power
company would be putting in their meters, they would have no issue with
each of those meter sockets being single phase for all tenants to get
120/240 from single phase dry transformers on each floor, even though
all other buildings in the same city would be 2 legged 120/208?
Beachcomber
There are many subtle factors that might affect this decision. If the
building is an elevator building, 3 phase might be desirable (if it is
available), even though 240V single phase elevators are also
available. Having just one outdoor 3-phase transformer connected with
a wye secondary that can supply the entire building might be the best,
cheapest, most economical way to go, if the load can be reasonable
balanced, central hot-water, common ventilation, etc.
As I stated in a previous thread, being a tenant in such a building
can be a pain if you personally have to deal with the installation of
208 volt ranges, dryers, hot-water heaters, etc. When I did live in
such a building, most of my neighbors didn't have a clue why it took 1
and 15 minutes to dry a load of laundry. This was considered a
luxury condo building too. A comparable rental building would be
more likely to have a common-area landlord provided laundry room.
This is the custom in the US for this type of housing in many major
cities.
If it is a low rise multi-unit multi-building setup, it is quiet
common in my current suburban area to go with the outdoor single/phase
pad-mounted transformers providing 120/240V. In this case, there are
no elevators or heavy HVAC loads and no common area service other than
low demand building lighting circuits. Everybody gets a meter and 150
or 200A service. Everyone gets there own electric range and hot water
heater. The downside? Cheap construction and
inexpensive-to-install, expensive to run radiant electric heaters that
the tenant pays to operate are commonly provided.
In a place like Chicago, there are a lot of high density, medium-rise
apartments of and no room for outdoor, individual pad mount
transformers. The transformers for these buildings are sometimes
placed in underground vaults or basements rooms and they sometimes
explode with an eruption of big black smoke. They are very expensive
to replace and sometimes result in extended outages.
Beachcomber
Of all the news stories I've seen of transformers in basements and under
the streets exploding, etc, I'd say nearly half seem to be in Chicago.
One I remember many years ago was at a very large single building dorm
at Illinois State in Bloomington. The transformer couldn't handle the
increasing electrical use of students, and one year, right as students
were all moving in and peaking demand because classes hadn't yet begun,
it blew. I read somewhere they had to actually dig the ground to build
an access to the basement to install the replacement, which was larger.
I heard the place was dark for a couple weeks. Whoever figured the loads
when the building was built had no idea of the future. Just how much
they should have provided for in growth may have been overshadowed or
overruled by state cost considerations. I'm sure they found a way to
charge all the students for the costs, and then charge the taxpayers at
the same time for the same costs.
Beachcomber
College dorms are a classic example of cheap wiring that gets quickly
overloaded. There are many such stories. The culprits a few years
ago were refrigerators and cheap 1000 watt halogen lamps. Everyone
brought one in because they provided a good reading light and didn't
cost too much. The dorms wiring systems got overloaded and many
colleges banned these types of lamps. A few years ago the Home Depot
stores were offering a turn-in-your-1000-watt halogen-lamp and buy a
fluorescent at a discount promotion.
Beachcomber
Ben Miller
In some cases the utility owns the transformer. They have their own load
factors that they use to size the distribution equipment, and they don't
always know when the loads have increased from the initial sizing. ComEd
came under a lot of fire in the Chicago area a few years ago after an
investigation found widespread lack of infrastructure maintenance.
Ben Miller
Where did all those 1000 watt halogen lamps end up? I'll take a dozen :)
Why do maintenance when you can make the profit sheet look better and give
the investors a larger dividend so the directors that won't fire you at
will can stay voted in, thus keeping your job and locking in that extra
10,000,000 share boosted option at retirement.
Matthew Beasley
I suspect it's a case of whether the utility was trying to tie into a
120/208 network or not. In many older cities, they would put a few
substations in a medium rise building and tie the building network 120/208
into the 120/208 network under the streets.
The whole network system is designed to provide reliable power back when
medium voltage transformers and cables weren't reliable. Now with the
reliability of equipment, it's no longer needed.
In newer areas, there isn't a network, it's all radial distribution from
each transformer. In that case it's likely they would be OK with 120/240
transformers.
There are several people warehouses (what I call the medium rise and high
rise apartments) going in nearby. You have piqued my curiosity. I do know
a utility guy that works for the supplying utility, I'll ask him about the
service. I'm suspecting it's dry type transformers every couple of floors
and we don't have a network in the city, it's all radial distribution.
| transformers.
Someone posted, perhaps here, a while back about some kind of issue with
a residence customer of a utility in a network area in some city. But the
network was, for some reason, 480Y/277. They ended up with 480 single
phase going into the house and a dry transformer stepping that doen to the
usual 120/240. I would think if it's a 480Y/277 network, they would have
to do that, or something like it, for everyone. But I also recall in the
post that it was a building that had zero exterior space for a transformer
outside. At least that would help reduce the available fault current on
the lower voltage side.
I also read in tariff document somewhere that Portland Oregon's downtown
network is 216Y/125. Maybe that's just because some of the wiring is a
bit long and that gives them a reserve to stay within the needed voltage
range (they might end up seeing 200Y/115 at the far end).
| By this you mean that multiple transformers have secondaries paralleled
| and the length between the farthest ends of a single 120/208V system can
| be quite substantial?
I see two reasons for how things are wired in high density areas. Beyond
the issue of the reliability that brought about the parallelism there was
the lack of adequate single space just anywhere designed to put in a MV to
LV station. Where space was available would not necessarily be where the
capacity was needed. Connecting it all together with reliable equipment
today could still be essential in city downtown areas.
Of course the largest buildings could have MV delivered through the core
to upper floors with a MV to LV step down room every few floors. Anyone
know what the voltage and current levels were going into the former World
Trade Center towers (a likely high end example)?
Matthew Beasley
Yes, from one end to the other the 120/208V network would be several miles.
Each street had 120/208V feeders running along it and the feeders were
cross-connected at every intersection. The cross connects were protected
by 'network protectors' which are short circuit protection only fuses.
Customers would be fed through taps at each street, also protected by
network protectors. All secondary work is done live.
Primary to secondary transformers would be placed where there was room. The
transformers had 'network relays' on the secondary that would disconnect the
transformer on reverse power flow. The network relay would reconnect power
when the transformer output was re-energized. There would be multiple
feeders to each area, and one of them could be de-energized without
disrupting a customer. This allowed work on the transformers or primary
feeders to be done without disrupting customers as long as it wasn't at peak
demand.
Once buildings started growing the voltage drop and required feeder size to
serve the building became a problem. This became even worse as electric
elevators came into use because the elevator motors were on the roof, far
from the service. The solution was to place a substation on the roof, and
interconnect it with the network. Usually at least two feeders would be
brought up and two transformers would be on the roof to allow continued
operation with one feeder out. Because the secondary conductors were not
short circuit protected, substantial fireproof ducts were required going up
to the roof. All of the feeders and transformers are owned by the utility,
and usually the transformer vaults are restricted to utility worker only
access. Services tap off the feeders at each floor, with metering through
current transformers. This allowed all of the meters to be centrally
located. It also allowed one meter to record for multiple services on
multiple floors if one tenant occupied more than one floor. As buildings
began to grow taller, mid building substations became common.
Newer buildings began to switch over to 277/480V when 277 volt fluorescent
lighting became available. This allowed the bulk power consumers of the
lighting, elevators and HVAC to all be powered from 277/480V with only the
wall outlets and other sundry devices to be powered through local stepdown
transformers. To supply the 277/480V, 'spot' networks were overlaid the
existing network. The spot networks usually fed a smaller area around the
tallest buildings in a downtown area. The spot networks usually had their
own feeders. Just like the 120/208 networks, the 277/480 networks usually
ran up a building with substations on multiple floors.
Don Kelly
The feeds would normally be paralleled and both in use. What you describe
for C-D-E-C is a loop and is commonly used. A City may have one or more
loops with local substations being fed from the loop. There is no point or
cost savings in having one section of line out of service unless it is
faulty or routine maintenance is needed.