Heat sensor in the attic

I would like to put a heat sensor in one of my attics. I have a
chemetronics 601 in my laundry room. What should I place in the attic.
Also I live in New Jersey.
 
F

Frank Olson

Jan 1, 1970
0
I would like to put a heat sensor in one of my attics. I have a
chemetronics 601 in my laundry room. What should I place in the attic.
Also I live in New Jersey.


The 604 is a fixed temp 200 degree heat detector. If you're considering
putting one up there, go with that. A RoR won't work in attics (even a high
temp one). You're liable to get some false alarms.
 
R

Robert L. Bass

Jan 1, 1970
0
The 604 is a fixed temp 200 degree heat
detector. If you're considering putting
one up there, go with that. A RoR won't
work in attics (even a high temp one).
You're liable to get some false alarms.

I disagree. The 602 (RoR) is designed for use in attics. I've installed
hundreds of them in attics with no problems at all. Attic temperature can
go high but it won't generally rise fast enough to set off a rate-of-rise
heat detector. Just be sure to use a detector that's rated for at least
190ºF. There are several brands which range from 194 to 200 degrees. They
all perform about the same.

--

Regards,
Robert L Bass

=============================>
Bass Home Electronics
2291 Pine View Circle
Sarasota · Florida · 34231
877-722-8900 Sales & Tech Support
http://www.bassburglaralarms.com
=============================>
 
F

Frank Olson

Jan 1, 1970
0
Robert L. Bass said:
I disagree. The 602 (RoR) is designed for use in attics. I've installed
hundreds of them in attics with no problems at all. Attic temperature can
go high but it won't generally rise fast enough to set off a rate-of-rise
heat detector. Just be sure to use a detector that's rated for at least
190ºF. There are several brands which range from 194 to 200 degrees.
They all perform about the same.

I've seen RoR detectors set off in attics. The issues disappeared when we
replaced them with fixed temps. The problem with attics is that they're
prone to humidity as well as heat (at least they are here) which plays havoc
with RoR's in time.
 
R

Robert L. Bass

Jan 1, 1970
0
I've seen RoR detectors set off in attics...

If the temperature exceeds the rating of the thermal sensor they go off but
that is equally true of fixed temperature heats.
The issues disappeared when we replaced
them with fixed temps. The problem with
attics is that they're prone to humidity as
well as heat (at least they are here) which
plays havoc with RoR's in time.

Use higher quality RoR's. I've been using them in attics for decades
without any problems at all.

--

Regards,
Robert L Bass

=============================>
Bass Home Electronics
2291 Pine View Circle
Sarasota · Florida · 34231
877-722-8900 Sales & Tech Support
http://www.bassburglaralarms.com
=============================>
 
F

Frank Olson

Jan 1, 1970
0
Robert L. Bass said:
If the temperature exceeds the rating of the thermal sensor they go off
but that is equally true of fixed temperature heats.


Use higher quality RoR's. I've been using them in attics for decades
without any problems at all.


Uh-huh... and how often have you actually tested their operation?? Just
because they haven't false alarmed (and aren't visible), I'll bet you're
*assuming* they're working. Our residential alarm contracts allow for an
on-site inspection and test of our customer's alarm system on an annual
basis. This costs the home-owner $50.00 and those that opt for it benefit
additionally because we never charge them for replacement of the control
panel's battery (when it becomes necessary). Otherwise it would be a $75.00
charge (including the battery and labour).
 
N

Nick Markowitz

Jan 1, 1970
0
Any time I used ror high temp or not I have had problems with falses. I
have never had a false with a fixed 200. Attics have fast air changes with
fans etc which cause the problem and trick the rate of rise units in
commercail buildings.
I have seen this in barns as well that store hay in there loft area .

--
Nick Markowitz Jr.
Owner
Markowitz Electic Protection
Private Industry Fire Investigator.
Qualified Electrical- Fire Alarm Contractor
Registered EPA Freon Recovery

Contributing Editor Pa. Firemans Magazine
Staff Editor www.securitymission.com
Senior Correspondant www.1strespondernews.com
Exclusive Correspondant www.nbfd.us
Contributor www.monyoughfire.com
Contract Broadcast Engineer WAVL 910 AM apollo Pa.

"To error is human to realy foul things up requires a computer"

Irish Diplomacy

The ability to tell a man to go to hell and he tells you how much he is
going to enjoy the trip.
 
R

Robert L. Bass

Jan 1, 1970
0
Our residential alarm contracts allow for an on-site inspection...

Our contract required an annual inspection and test which was included in
our annual fee. We charged ~$20 to replace the control panel battery when
needed.

--

Regards,
Robert L Bass

=============================>
Bass Home Electronics
2291 Pine View Circle
Sarasota · Florida · 34231
877-722-8900 Sales & Tech Support
http://www.bassburglaralarms.com
=============================>
 
R

Robert L. Bass

Jan 1, 1970
0
Any time I used ror high temp or not I have had problems with falses. I
have never had a false with a fixed 200. Attics have fast air changes with
fans etc which cause the problem and trick the rate of rise units in
commercail buildings.
I have seen this in barns as well that store hay in there loft area .

Having never installed a fire alarm in a barn, I can't dispute that.
However, I've used ROR detectors in commercial and residential apps for
decades and they gave no problems. Besides, attic exhaust fans only lower
the attic temperature. A sudden *decrease* does not trip an RoR. That's
not how they work.

--

Regards,
Robert L Bass

=============================>
Bass Home Electronics
2291 Pine View Circle
Sarasota · Florida · 34231
877-722-8900 Sales & Tech Support
http://www.bassburglaralarms.com
=============================>
 
R

Robert L. Bass

Jan 1, 1970
0
Norm Mugford said:
The law as quoted by Mr. Bass:

"However, I've used ROR detectors in commercial and residential apps for
decades and they gave no problems".

That was just a statement of experience. Try reading the post next time.
 
N

Norm Mugford

Jan 1, 1970
0
The law as quoted by Mr. Bass:

"However, I've used ROR detectors in commercial and residential apps for
decades and they gave no problems".


Norm Mugford
 
N

Nick Markowitz

Jan 1, 1970
0
Obviously you have not worked with the same amount of heat travelling thru
roofs with big exhaust fans i have
The flash of heat cuased by the air movement causes the false as it begins
to pull extremely hot air thru the cooler area where multiple restaurant
hoods and other high heat process hoods peneatrate the roof void areas .
the units say right on them avoid areas were temp changes rapidly.
I had a problem particularly were industrial furnaces and kilns are
involved. put in the fixed 200 and never had another problem.

--
Nick Markowitz Jr.
Owner
Markowitz Electic Protection
Private Industry Fire Investigator.
Qualified Electrical- Fire Alarm Contractor
Registered EPA Freon Recovery

Contributing Editor Pa. Firemans Magazine
Staff Editor www.securitymission.com
Senior Correspondant www.1strespondernews.com
Exclusive Correspondant www.nbfd.us
Contributor www.monyoughfire.com
Contract Broadcast Engineer WAVL 910 AM apollo Pa.

"To error is human to realy foul things up requires a computer"

Irish Diplomacy

The ability to tell a man to go to hell and he tells you how much he is
going to enjoy the trip.
 
R

Robert L. Bass

Jan 1, 1970
0
The flash of heat cuased by the air movement
causes the false as it begins to pull extremely
hot air thru the cooler area where multiple
restaurant hoods and other high heat process
hoods peneatrate the roof void areas.

What you describe is a very different environment from the typical attic.
IMO it is not a valid basis for a decision not to ever use RoR detectors in
attics.

--

Regards,
Robert L Bass

=============================>
Bass Home Electronics
2291 Pine View Circle
Sarasota · Florida · 34231
877-722-8900 Sales & Tech Support
http://www.bassburglaralarms.com
=============================>
 
C

Crash Gordon®

Jan 1, 1970
0
I also put 200 fixed in garages as well.

It get's really hot out here.
 
N

Nick Markowitz

Jan 1, 1970
0
I have not hadthem pop in a normal gargae but have had accidental trips body
shop garages when there gas welding
below one .

--
Nick Markowitz Jr.
Owner
Markowitz Electic Protection
Private Industry Fire Investigator.
Qualified Electrical- Fire Alarm Contractor
Registered EPA Freon Recovery

Contributing Editor Pa. Firemans Magazine
Staff Editor www.securitymission.com
Senior Correspondant www.1strespondernews.com
Exclusive Correspondant www.nbfd.us
Contributor www.monyoughfire.com
Contract Broadcast Engineer WAVL 910 AM apollo Pa.

"To error is human to realy foul things up requires a computer"

Irish Diplomacy

The ability to tell a man to go to hell and he tells you how much he is
going to enjoy the trip.
 
N

Nick Markowitz

Jan 1, 1970
0
I have had RoR pop in conventional attics as well .
And being a fireman I can tell you I have seen more than my share of them
over the years go off.
yet i have had attics with 135 RoR and they never falsed.
it all apears to be design of the attic and physical size plus the type of
roof and how it is vented as to it causing a problem or not.

Nick Markowitz Jr.
Owner
Markowitz Electic Protection
Private Industry Fire Investigator.
Qualified Electrical- Fire Alarm Contractor
Registered EPA Freon Recovery

Contributing Editor Pa. Firemans Magazine
Staff Editor www.securitymission.com
Senior Correspondant www.1strespondernews.com
Exclusive Correspondant www.nbfd.us
Contributor www.monyoughfire.com
Contract Broadcast Engineer WAVL 910 AM apollo Pa.

"To error is human to realy foul things up requires a computer"

Irish Diplomacy

The ability to tell a man to go to hell and he tells you how much he is
going to enjoy the trip.
 
C

Crash Gordon®

Jan 1, 1970
0
hot garage, homeowner drives in with a hot engine...had it happen a few times, then switched to fixed and never had probs after that.
 
N

Norm Mugford

Jan 1, 1970
0
Mr. Bass did you read that.

Per Mr. Markowitz.......

"yet i have had attics with 135 RoR and they never falsed.
it all apears to be design of the attic and physical size plus the type of
roof and how it is vented as to it causing a problem or not".

Ha, Ha, Ha, Ha, Ha, Ha,,,,,,I'm rolling on the floor.....

How many years experience did you say you have Mr. Bass
minus of couse the years in the Big House.......
minus the years in Florida .......6 years I believe.
minus the years in drug induced stupor........

Norm Mugford
 
A

Allan Waghalter

Jan 1, 1970
0
Norm,
You don't sound much like a state official in your postings about RLB. I
think you have let him get under your skin and cloud your usual clear
thinking. Go back and read your postings.... Everytime you get off on Bass,
you stoop to a level lower than the one you occuse him of being.
Allan
 
R

Robert L. Bass

Jan 1, 1970
0
I'm rolling on the floor.....

Alcohol can do that to you.
 