Surge Protectors
Jeffrey D Angus
William said:
Uh... In the MOV?
I thought the MOV conducted above its breakdown voltage (generally around
300V), and the energy in the section of the AC waveform above that voltage
heated up the MOV.
Am I missing something?
In your typical plug in suppressor mounted next to the computer
for example. The job of the MOV is to clamp the maximum voltage
across the "protected" outlets. That it does this fairly quickly
is what hopefully protect the equipment, while at the same time
drawing enough current through the house wiring to either pop
the fuse or circuit breaker at the suppressor or back at the
service panel.
What the plug-in suppressors rely on is the impedance (generally
inductive) in the house wiring to limit the rise time of the
surge until the circuit breaker (or fusable parts) have time to
react by opening up.
The term joules can be described as Watt Seconds. And the ability
to deal with it is based on the fault (or surge) being over, or
the circuit breakers upstream open before the device self
destructs.
Whole house protectors work the same way in that they shunt the
current to ground safely before it has a chance to cause a
destructive rise to the rest of the house wiring.
Jeff
W
William Sommerwerck
Ohm's Law:
If the MOV conducts at a low resistance, the power it dissipates will be
minimal. Thus, the surge energy gets dissipated in whatever ground it's
shunted to.
How low is low?
I suspect that's not a complete explanation, but I won't argue at this time.
Cydrome Leader
William Sommerwerck said:
Uh... In the MOV?
heated up the MOV.
Many years ago, PC and/or Byte (I forget which) used to test suppressors. If
they failed to provide suppression, I assume the mag would have said so.
hillarious, PC magazine is your source for the lowdown on surge supression
devices?
Sjouke Burry
Jim said:
Ohm's Law.
If the MOV conducts at a low resistance,the power it dissipates will be
minimal.
Thus,the surge energy gets dissipated in whatever ground it's shunted to.
Bullshit. The Mov dissipates (Umov)*I*T, or
Total Energy=MOVvolts * Current * Seconds.
Or integrate over those values, if they vary in time.
The Mov voltage does NOT drop to zero, when conducting.
Where did you learn about electricity??????
Of course some currents might be enough to blow the MOV,
and that is specified in the documentation, as in how
many WATTseconds blows it to pieces.
Even then it still might provide protection, although
only once, and then blow the mains fuse.
W
William Sommerwerck
If
devices?
It was, 20 years ago. I don't think you get the point, though.
David
I never said it did.
the MOV voltage rating is the voltage when it changes
state and drops to a
low resistance to shunt the surge to GROUND.
Now,how low a resistance in the conducting state is
another matter.
that's dependent on the MOV design/ratings.
USAF PME School,1971.
yes,I said the MOV's dissipation would be
"minimal",....compared to the
total energy the MOV was passing to ground.
what energy the MOV dissipates can easily be enough to
blow it apart.
I've seen it happen many times.
But the MOV is not dissipating the total energy of the
surge with it's
suicide.
Jim Yanik
jyanik
at
localnet
dot com
A MOV is somewhat like two back-to-back Zener diodes. It is
a voltage clamp. You do not pass energy to ground, you pass
current to ground just like you do with any load. The energy
is totally dissipated in the MOV.
David
Cydrome Leader
So what is the point? John Dvorak wrote a story about surge supressors and
how they worked with his Cumulus 386 laptop and his CompuAdd 486sx tower?
W
William Sommerwerck
The point is that they were performing lab tests on the suppressors. These
tests included determining the clamping voltage. (I don't remember if they
were tested to destruction.) The tests were presumably performed in
accordance with industry-accepted standards.
bud--
westom said:
Your job is to promote plug-in protectors.
Poor westom just keeps repeating the same lies, just like Josef Goebbels.
If he had valid technical arguments he would not have to try to
discredit those that expose his drivel.
My only association with surge suppressors is that I have 2 of them.
You
cannot even post any spec numbers that define protection from each
type of surge.
"Each type of surge" is more nonsense. SquareD, amongst others, does not
have specs for "each type of surge".
I provided a link to the specs I have provided in many threads -always
ignored by westom, just like he ignores anything that conflicts with his
religious belief in earthing.
Apparently poor westom believes plug-in suppressors do not work, so he
believes specs cannot possibly exist.
Destructive surges are hundreds of thousands of joules. Where does
that energy dissipate? Bud says that energy just magically
disappears.
Poor westom's religious blinders prevent him from seeing what has been
said in this thread, and numerous other threads.
For incoming power wires, at about 6kV there is arc over from service
busbars to the enclosure. After the arc stabilized the arc is hundreds
of volts. The enclosure is connected to the earthing electrodes, so this
dumps the vast majority of the incoming surge energy to earth. The
neutral (in the US) is also always tied to the system ground at the
service, so energy coming in on the neutral is directly earthed.
Apparently that is all magic for westom.
For a plug-in suppressor, the impedance of the branch circuit wiring
greatly limits the current that can reach the suppressor. That greatly
limits the energy that can reach the suppressor. NIST surge guru
Martzloff looked at the energy that could reach the suppressor and was
surprised that it was 35 joules or less. In most of his tests it was
under 1 joule. That is with service surges up to the maximum that there
is any reasonable probability of occurring.
As Sjouke wrote, the MOV dissipates an energy equal to the clamp voltage
times the current times the time. For a plug-in suppressor the current
is very limited by the branch circuit impedance. And the time is very
short - well under 100 microseconds. Fuses or circuit breakers do not
provide protection because they are nowhere near fast enough - they
won't open during a surge.
Plug-in suppressors do not work primarily by earthing a surge - that
reason poor westom believes they do not work. The IEEE surge guide
explains how they work (starting pdf page40). They clamp the voltage on
all wires to the ground at the suppressor. The voltage between all wires
going to the protected equipment is safe for the protected equipment.
Service panel suppressors also work by clamping the voltage - from hot
wires to ground/earthing electrode (and hot-to-hot). Because the current
can be up to 10,000A per hot (essentially zero probability of higher
current, at least for houses) they can dissipate significant energy. But
the vast majority of the energy is dissipated in the earth by the
service earth electrode connection. The largest surges (lightning) are
under 100 microseconds. Suppressors are readily available that will
provide protection. With thousands of amps to the earthing electrode,
the potential of the building "ground" can rise far above "absolute"
earth potential.
Neither service panel suppressors or plug-in suppressors protect by
absorbing the surge energy. But in the process of protecting, some of
the energy is absorbed.
MOVs are fast enough to protect from the fastest surge. And if there was
an extremely fast rise time it would be lowered by the impedance of the
source wiring.
All of the above is from NIST expert Martzloff, or other experts in the
field.
westom ignores it all.
Bud's citation Page 42 Figure 8 shows a surge earthed 8000 volts
destructively through a nearby TV.
The lie repeated. Poor westom tries to make an example that explains
protection say the opposite.
The plug-in suppressor in this IEEE surge guide example protects the TV
connected to it. It lowers the surge voltage at a second TV, although
its job is to protect the equipment connected to it. It is a lie that
the suppressor at TV1 damages TV2.
The point of the illustration for the IEEE, and anyone who can think, is
"to protect TV2, a second multiport protector located at TV2 is required."
Why?
The house did not earth via a 'whole
house' protector.
In the IEEE example the surge comes in on the cable service, and high
voltage results from a ground wire that is too long. westomn's favored
service panel suppressor would provide absolutely *NO* protection. The
IEEE says, for distant entrance points, that "the only effective way of
protecting the equipment is to use a multiport [plug-in] protector."
A protector is
only as effective as its earth ground.
westom's religious mantra protects him from conflicting thoughts (aka
reality).
westom is the poster child for cognitive dissonance.
Still never explained - why aren't flying airplanes crashing every day
when they are hit by lightning?
He is paid to
The lie repeated.
But still never seen - any reliable source that agrees with westom that
plug-in suppressors are NOT effective.
Still never seen - answers to simple questions:
- Why do the only 2 examples of protection in the IEEE guide use plug-in
suppressors?
- Why does the NIST guide says plug-in suppressors are "the easiest
solution"?
- Why does the NIST guide say "One effective solution is to have the
consumer install" a multiport plug-in suppressor?
- How would a service panel suppressor provide any protection in the
IEEE example, page 42?
- Why does the IEEE guide say for distant service points "the only
effective way of protecting the equipment is to use a multiport
[plug-in] protector"?
- Why did Martzloff say in his paper "One solution. illustrated in this
paper, is the insertion of a properly designed [multiport plug-in surge
suppressor]"?
- Why does Dr. Mansoor support multiport plug-in suppressors?
- Why does "responsible" manufacturer SquareD says "electronic
equipment may need additional protection by installing plug-in
[suppressors] at the point of use"?
- Why don’t favored SquareD service panel suppressors list "each type of
surge"?
For real science read the IEEE and NIST surge guides. Both say plug-in
suppressors are effective.
The IEEE guide, in particular, is really an excellent source of
information from a reliable source. I really recommend anyone who is
interested in surge protection read it.
Jeffrey D Angus
David said:
Amazing coincidence that they act much like the old NE-2 neon
bulb across the antenna leads of old receivers for protection.
They would conduct around 65 volts and suddenly go to near
zero impedance, safely shunting what ever energy on the antenna
line to ground.
And although most receiver inputs couldn't handle a steady state
of 65 volts (or 130 vpp), they could handle them long enough for
the neon bulb to conduct and then shunt them to ground.
Jeff
David
Uh,"passing current to ground" IS passing energy to
ground.
http://en.wikipedia.org/wiki/Metal_oxide_varistor
Varistors can absorb part of a surge. How much effect this
has on risk to
connected equipment depends on the equipment and details
of the selected
varistor. Varistors do not absorb a significant percentage
of a lightning
strike, as energy that must be conducted elsewhere is many
orders of
magnitude greater than what is absorbed by the small
device.
This is my final say on this topic. In the quote above, you
assume the section saying that "... energy that must be
conducted elsewhere ..." goes to ground through the MOV.
This is where your error resides. The energy is going
elsewhere but being dissipated somewhere else completely
such as blowing up a transformer. The article should also
use the term dissipated elsewhere to make things clearer.
You also assume that passing current is equivalent to
dissipating energy. Current can *move* energy somewhere, but
electrical energy is only dissipated when the current causes
a voltage drop. A perfect ground will not have a voltage
drop so that is not where the the energy is being
dissipated.
David
bud--
westom said:
And why Bud will not discuss wire
impedance and earth ground.
Poor westom's religious blinders prevent him from reading what gets
written. I certainly have written about wire impedance in this thread.
But if westom was not hampered by religious blinders he would read in
the IEEE surge guide that plug-in suppressors do not work primarily by
earthing. They work primarily by clamping the voltage on all wires to
bud's citation Page 42 Figure 8 shows a plug-in protecting earthing
a surge 8000 volts destructively through a nearby TV. He hopes you do
not grasp the point in his IEEE citation.
I hope everyone will "grasp the point" in the IEEE example.
- The TV connected to the plug-in suppressor is protected.
- "To protect TV2, a second multiport protector located at TV2 is required."
So let's put numbers to it. Let's say the plug-in protector and TV
are 50 feet of wire from the breaker box. That means it is less than
0.2 ohms resistance. And maybe 120 ohms impedance. So that protector
will earth a trivial 100 amp surge? 100 amps times 120 ohms means the
protector and TV are at maybe 12,000 volts.
With minimal reading skills westom would have read that at about 6kV
(US) there is arc-over at the service panel from bus to enclosure/ground
- which is connected to the earthing electrode and neutral. After the
arc is established, the voltage is hundreds of volts. The same thing
happens at receptacles. This is a well established action for people who
are familiar with surge protection.
westom makes up a 100 amp surge on the branch circuit and 120 ohm
impedance - won't happen together.
Why did the protector
earth that surge 8000 volts through the TV?
And the lie repeated - 5th time?
In the IEEE example - of how plug-in suppressors protect - the
suppressor at TV1 causes absolutely NO damage to TV2.
Why do telcos all over the world not waste money on bud's plug-in
protectors?
Ho-hum - because telco switches are high amp, hard wired, and thousands
of phone circuits would have to go through the plug-in suppressor.
Learn that no protector works by absorbing energy.
True of service panel and plug-in suppressors (but they absorb some
energy while protecting).
If you put a MOV across a relay coil, it protects by absorbing energy.
That is why the
protector too close to appliances and too far from earth ground can
even earth that surge 8000 volts destructively through a nearby TV.
The lie repeated - 6th time?
In the IEEE example the surge comes in on the cable service.
westom has not explained how his service panel suppressor would provide
any protection.
That is because it would provide absolutely NO protection.
With separated service entry points the IEEE guide says "the only
majority only believe the advertising myths - that protectors
magically make hundreds of thousands of joules just magically
disappear.
Only magic if you suffer from willful stupidity.
IOW a protector
is only as effective as its earth ground.
Ho-hum - still never explained - why aren't flying airplanes crashing
every day when they are hit by lightning? They must drag an earthing chain.
Still missing - any reliable source that agrees with westom that plug-in
Still missing - answers to simple questions:
suppressors?
solution"?
suppressor]"?
surge"?
bud--
Jim said:
feel free to edit it.
No,that's what YOU assume I said. Wrongly.
HA,now you're talking about "perfect grounds".Sheesh.
you don't know what you're talking about.
I agree. The vast majority of energy in a lightning strike is passed on
to the earth.
Assume a surge of 10,000A on a service wire (maximum that has a
reasonable probability), a very good resistance to earth of 10 ohms and
a duration of 100 microseconds. If I am multiplying right that is
100,000 joules dissipated in the earth.
If you had a service panel suppressor with UL let through voltage of
330V (measured at a specified current much lower than 10kA) the actual
voltage across the MOV might be 500V and the energy dissipated for the
same surge would be 500 joules.
Most of the energy that was available at the cloud is dissipated on the
trip down - in heat, light, sound....
In about any lightning strike there are multiple paths to earth -
multiple utility earthing points, multiple houses, ....
BTW,when a lightning strike hits a ground,it dissipates it's energy -in the
ground-. literally.
Nice example.
bud--
Jim said:
"clamping" is a misuse of the word WRT surge protectors.
It misleads people,as in "david" s post.
"trigger voltage" might more accurate.
MOVs have a smooth, but nonlinear, curve from not conducting at low
voltage to high conduction current at higher voltages. They do not
"trigger" like a neon light. And the voltage across the MOV does not
suddenly decrease, like it would in a neon light (you probably didn't
say it did). "Clamping" is a widely used term, including the wiki
article on MOVs. (Gas discharge tubes are like a neon light, and do
trigger.)
One of the parameters for a MOV is MCOV (maximum continuous operating
voltage) which is the voltage at which the current is 1 mA. The
increase in current is smooth (but very non-linear) above the MCOV, just
like it was smooth (and non-linear) below the MCOV.
(When the MCOV for a MOV decreases 10% it is the defined end of life for
a MOV - referred to in the wiki article.)
A MOV is very much like back-to-back Zener diodes, but does not clamp as
sharply. But MOVs have huge current capacity in a small package.
The clamp voltage that is usually cited is the UL let through voltage
(UL calls it something a little different). This is the voltage at a
specified test surge current. If the surge current goes up, the let
through voltage will be higher (in a non-linear way).
bud--
westom said:
Bud promotes plug-in protectors. It is his job.
westom just continues to repeat the same lies - a la Goebbels.
And the same misrepresentations - a la religious fanaticism. All the
sources westom uses, including even his favorite manufacturers, say
plug-in suppressors are effective.
In particular, the IEEE and NIST surge guides both say plug-in
suppressors are effective. Links have been provided to these reliable
sources.
There are 259,615,938 other web sites, including 23,843,032 by lunatics,
and westom can't find another lunatic that says plug-in suppressors are
NOT effective.
Also still missing - answers to simple questions:
suppressors?
solution"?
suppressor]"?
- Why aren't airplanes crashing daily when they get hit by lightning (or
do they drag an earthing chain)?
surge"?
Why can't you answer simple questions westom????
GregS
Assuming they are MOV based, read MOV datasheets to learn how MOVs
work and obtain relevenant numbers for the test. Perform a 1
milliamp test to confirm these numbers on that protector. This test
is described in some manufacturer application notes.
The test only confirms the protector can conduct. Does not say
anything about what makes a protector effective - the earth ground and
how it connects to earth. The best surge protection in the world can
be useless if grounding is not done properly.
IEEE 587 and UL 1449 Talks of 3-6KV and 500 amps typical
test produces eventual failure.
greg
GregS
My news reader sees a problem in these postings
Mark Waller wrote an article for Byte.
I have his book PC Power Protection from 1988.
Great reading. I should also have that mag article if
anybody is interested. I should look it up.
From worrying too much about protection, Mark is now a Family
Therapist.
Here is the article.
http://zekfrivolous.com/misc/waller.pdf
bud--
westom said:
An honest bud would simply post numeric specs to prove what he
claims.
An honest westom would admit that specs have been provided often in
other threads, and through a link in this thread. And also by other
people. Always ignored.
An honest westom would admit that both the IEEE and NIST surge guides
say plug-in suppressors are effective.
An honest westom would not try to make sources say the opposite of what
they actually say.
An honest westom would admit he can't find another lunatic that agrees
that plug-in suppressors are NOT effective.
An honest westom could answer simple questions:
suppressors?
solution"?
suppressor]"?
surge"?
Why don't you ever answer questions westom???