I'd like to check the basics of the calculations with you folks.
Discounting inefficiencies for the moment, how does the following sound?
Say I have 2 x 60 watt bulbs that I want to run on pv. That's a 120 Watt load (1 amp ac).
If I had a hypothetical 120 watt pv panel, with an average of 2.5 hrs of winter sunshine, then I should be able to power those lights for 2.5 hrs a day.
To run the load at night or during inclement weather, we go to batteries. 1 am ac would result in a 10 amp dc flow at 12V. A 150 ah battery should only be discharged to 50%, yielding an available 75 ah. Divided by 10 amps dc, the battery would be good for 7.5 hrs of operation.
Now if I had 2 batteries, in parallel, there would now be 15 hrs available. If the batteries were in series instead, there would still be 15 hrs available but the current flow would be halved, and the wiring size could be reduced. Of course the inverter would have to be for the correct voltage.
Back to the panel. The 120 watt panel wouldn't produce 12v x 10 amps, it would actually ring in around 17V with the current reduced accordingly. That's where an mppt controller comes in, essentially bringing the voltage back to 12 and the current up to 10.
Ok. How did I do?
As for system sizing, the tendancy is to want to be sized for 100% pv at all times, but if I size for winter sun, I'll have tons of excess in the summer. It would seem to make more sense to size for summer yields and supplement with the gen in the winter.
A question about inefficiencies. I've seen some places use 85% for inverters, batteries, wiring, and I'm not sure what all else. Resulting in almost doubling the panel size. Good practice or old data?
Ok. Fire away. Be nice!
Discounting inefficiencies for the moment, how does the following sound?
Say I have 2 x 60 watt bulbs that I want to run on pv. That's a 120 Watt load (1 amp ac).
If I had a hypothetical 120 watt pv panel, with an average of 2.5 hrs of winter sunshine, then I should be able to power those lights for 2.5 hrs a day.
To run the load at night or during inclement weather, we go to batteries. 1 am ac would result in a 10 amp dc flow at 12V. A 150 ah battery should only be discharged to 50%, yielding an available 75 ah. Divided by 10 amps dc, the battery would be good for 7.5 hrs of operation.
Now if I had 2 batteries, in parallel, there would now be 15 hrs available. If the batteries were in series instead, there would still be 15 hrs available but the current flow would be halved, and the wiring size could be reduced. Of course the inverter would have to be for the correct voltage.
Back to the panel. The 120 watt panel wouldn't produce 12v x 10 amps, it would actually ring in around 17V with the current reduced accordingly. That's where an mppt controller comes in, essentially bringing the voltage back to 12 and the current up to 10.
Ok. How did I do?
As for system sizing, the tendancy is to want to be sized for 100% pv at all times, but if I size for winter sun, I'll have tons of excess in the summer. It would seem to make more sense to size for summer yields and supplement with the gen in the winter.
A question about inefficiencies. I've seen some places use 85% for inverters, batteries, wiring, and I'm not sure what all else. Resulting in almost doubling the panel size. Good practice or old data?
Ok. Fire away. Be nice!