Re (3): UPS with earth leakage device.
Em Quinta 07 Janeiro 2010 08:27, [email protected] escreveu:
You are confusing a UPS with a emergency electric generator; those are the
ones that start working after the power goes off.
A UPS needs to keep the power up without letting it go down even for a split
second.
Let's be more scientific: at 50 Hz, there are zero-crossings every 10 ms.
The only switch a ups does when the power goes off is that it stops charging
the batteries. The output of a UPS is allways given by the same circuits
regardless if the power is on or off
with power on:
main power -> AC-DC converter -> DC-AC converter -> output
-> charge batteries.
with power off:
batteries -> DC-AC converter -> output
this is the only way that an ups can keep the output on without any breaks.
So the computer is fed from the UPS *always*,
and the "switch over is only from (accum to ) or (mains to D2A) ?
M-A2D-D2A->C
----B-D2A->C
so resuming: if the ups's output is given the wrong voltage, frequency,
sinosoidal wave, etc... you have two choices:
1- repair the ups
2- replace the ups.
What did I write to suggest that "the ups's output is given the wrong" output ?
How would that cause the earth-leakage to activate ?
philo said:
So the conclusion is reversed from what has happened
It was a ground fault which *caused* the power interruption.
The UPS simply was on because the "mains" breaker had tripped
No it's a chain of events over a few milliseconds.
The UPS detects that the mains is 'abnormal' and switches;
which causes an earth-leakage abnormality.
My problem is that since the earth-leakage AFAIK is mechanical,
it should not react to the spike caused by the UPS.
What are typical earth leakage response times?
if you have electrical questions, it's better to put them in
sci.electronics.basics
yes, the boys here are just guessing.
i can tell you that if you desconnect the earth, ther will be no more a
neutral in the output, you will have two live lines with a voltage
between them, and that could cause other issues.
Yes disabling the earth-leakage-detector is not good.
david wrote:-
This is only true with a double-conversion type UPS, which most cheap PC-
type UPS's are not. Most cheap UPSs have a transfer switch in them, so
the power is actually interrupted for a few milliseconds when the mains
fail.
Yes, I'd expect the computer PSU to 'hold over' for 2 cycles: 20 ms.
It seems that none of you are considering the interaction back to the
earth-leakage ?
== Thanks for any reasoned answers [not guesses].